Thread: Wiring of pump controller

  1. #1
    New Member
    Join Date
    Apr 2015
    Location
    CT
    Posts
    3
    Thanks
    5
    Thanked 0 Times in 0 Posts

    Wiring of pump controller

    Click image for larger version. 

Name:	wire.jpg 
Views:	15528 
Size:	42.6 KB 
ID:	5469

    Hi guys, my first post although I have browsed your great forum many times.
    I need to wire a new pump controller (switching pump on and off depending on the pressure)

    The connections on the controller is as follows:

    E
    L
    N

    and

    E
    U
    V

    Obviously the mains go to E (earth), L (Live) & N (Neutral) and E, U and V goes to the pump

    Could you please advise how to connect the pump (U & V) Single phase having the L, N and E

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    It seems that the controller assumes you have a capacitor start and run motor with a built in mechanism to take care of the start capacitor, which you generally will not find with a submersible pump.
    The U and V connections from the controller would simply go to the 2 wires of your motor supply cable.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. Thanks given for this post:

    viljoenp (09-Apr-15)

  4. #3
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    Good day Viljoenp

    It should not matter which way around the L & N of your pump wires goes since it is AC.

    Maybe to be safe confirm which connection is L by having the controller switch on an see between U and Earth and the V and Earth which one gives you 220v also just for interest sake check continuity between Earth in & Earth out so make sure it is internally bridge or if you should put a bridge in yourself.

    "I used to have a lot of anger issues, now I just have a passion for justice"

  5. Thanks given for this post:

    viljoenp (09-Apr-15)

  6. #4
    New Member
    Join Date
    Apr 2015
    Location
    CT
    Posts
    3
    Thanks
    5
    Thanked 0 Times in 0 Posts
    Hi, thank you very much. I have tried all options and the fault light on the controller stays on and the controller does not work. I have discarded this new automatic controller type system and went back to the old fashion pump with tank and pressure switch.

  7. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Is the controller specified for the pump and motor that you are attempting to run. There is no one controller fits all, they are all specifically designed for a set of pump and motor, if not it will not know when an overload is taking place, or when there is an under load taking place to to no water, in in some cases depending on the quality of the pump, when the outlet is blocked.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. Thanks given for this post:

    viljoenp (10-Apr-15)

  9. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The diagram shown is just a 2-pole switch, it's switching the live and the neutral of the pump supply as it's shown. It should be compatible with any single phase pump which has a running current equal or less that the AC3 rating of the switch contacts.
    _______________________________________________

    _______________________________________________

  10. Thanks given for this post:

    viljoenp (10-Apr-15)

  11. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    There is usually another label with the rating of the equipment either on the outside lid or side of the box.
    The diagram label is a generic label, and has no specifications on it.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  12. Thanks given for this post:

    viljoenp (10-Apr-15)

  13. #8
    New Member
    Join Date
    Apr 2015
    Location
    CT
    Posts
    3
    Thanks
    5
    Thanked 0 Times in 0 Posts
    According to the specifications, this controller can be used on any pump as long as the pressure does not go beyond 10 bar. It can even be used on a three phase pump in which case the wiring is as per the following diagram. Thanks for all inputs. Click image for larger version. 

Name:	pump c.jpg 
Views:	15429 
Size:	53.1 KB 
ID:	5479

  14. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    So what was the fault indicating?
    No pressure?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  15. #10
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    Well with this diagram it makes perfect sense...

    The controler feeds the contactor's coil and the contactor feeds the motor.

    As long as your contactor has a 220v coil the controler can switch the contactor. As for the motor depending on the supply circuit it can be anyone of the 2.

    "I used to have a lot of anger issues, now I just have a passion for justice"

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Wiring under thatch
    By camrad in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-17, 05:32 AM
  2. open wiring
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 48
    Last Post: 29-Nov-14, 09:25 AM
  3. Pump with Pressure Tank ???
    By tec0 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 03-Nov-13, 10:52 AM
  4. [Opinion] What type of wiring?
    By 123 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Apr-10, 11:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •