    And if there is no center tap to earth?

    I can't help wonder if many of the gensets out there are not actually V-O-V with a center tap to earth, but actually "safe supply" arrangements.
    Last edited by Dave A; 01-May-18 at 07:10 AM.

  2. #62
    New Member
    Join Date
    Jan 2016
    Location
    Cape Town
    Posts
    7
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Dave A View Post
    And if there is no center tap to earth?

    I can't help wonder if many of the gensets out there are not actually V-O-V with a center tap to earth, but actually "safe supply" arrangements.
    As I said (save for a few special builds) almost every generator under 7KVA is V-O-V (PNP). they are not designed for use as standby sets but rather as temporary supply via a lead. As long as your not connecting to the DB or feeding into the building supply in any other way these are legal, but the second you feed into the building they become illegal because there is no way you can bond the Neutral to the earth.

    What amasses me is that there are so many of these illegal installations, and they are being done by registered electricians and neither the ECA or the ECB have made any effort to stop this or to advice the public of the dangers.

  3. #63
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,300
    Thanks
    3,235
    Thanked 2,634 Times in 2,219 Posts
    Blog Entries
    12
    With respect, that doesn't answer the question.

    My 5.5 kVA generator doesn't have a center tap to earth.
    In fact there is no connection between the earth point of the generator and the single phase supply it provides. (Insulation test between earth and phase exceeds 1 Mega Ohm).
    Am I prohibited from connecting this generator to an electrical installation as an alternate supply?

  4. #64
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    327
    Thanks
    16
    Thanked 38 Times in 35 Posts
    I have been asked to connect up a generator which I have not seen yet and this was going to take place this morning.
    I have never connected a generator before because of the absolute minefield it has become, not to mention the confusion. However, I have taken an interest recently due to today's job and I am just wondering, are the regulations the same in version three of 101421 as they were in version 2, regarding the generator? I have yet to purchase version 3.
    Also,I noticed on the SABS website that there is a separate PDF available which deals entirely with the installation of generators. Has anybody purchased this separate PDF and and does it give clear concise instructions?

  5. #65
    Gold Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    581
    Thanks
    32
    Thanked 66 Times in 64 Posts
    Check your local municipality by laws as well.

    Here in our valley we need to apply and get permission from the Munic to do a generator installation.
    Technical specs of generator, circuitry and drawings of same are needed to accompany the application.

    Attached is a copy of our by laws, but I suggest you check those in your area before doing the job.

    https://www.buffalocity.gov.za/folder.php?id=sSWeUsCZg


    Peace out ... Derek.

  6. #66
    Gold Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    533
    Thanks
    12
    Thanked 131 Times in 110 Posts
    Quote Originally Posted by Leecatt View Post
    I have been asked to connect up a generator which I have not seen yet and this was going to take place this morning.
    I have never connected a generator before because of the absolute minefield it has become, not to mention the confusion. However, I have taken an interest recently due to today's job and I am just wondering, are the regulations the same in version three of 10142—1 as they were in version 2, regarding the generator? I have yet to purchase version 3.
    Also,I noticed on the SABS website that there is a separate PDF available which deals entirely with the installation of generators. Has anybody purchased this separate PDF and and does it give clear concise instructions?
    Besides a note added under 7.12.3.1.3 it is basically identical
    I have not seen the generator installation standard


    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together (see
    figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected (see also
    6.1.6).
    NOTE Where four pole switching is implemented, consideration should be given to use
    overlapping neutral switching devices
    .

  7. #67
    Gold Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    581
    Thanks
    32
    Thanked 66 Times in 64 Posts
    Tested a generator this morning. The specific model ...... Ryobi rg 6900K.

    Results as follows:

    No load ..... L - N 235V ; L - E 160V ; E-N 75V

    With load .... L - N 235V ; L - E 235V ; E-N 0V

    Is there anyone who can explain this. I'm wracking what's left of my brain cells but cannot understand it.

    Peace out .. Derek

  8. #68
    Junior Member rh1's Avatar
    Join Date
    Dec 2017
    Location
    Cape Town
    Posts
    16
    Thanks
    0
    Thanked 1 Time in 1 Post
    Quote Originally Posted by Derlyn View Post
    Check your local municipality by laws as well.

    Here in our valley we need to apply and get permission from the Munic to do a generator installation.
    Technical specs of generator, circuitry and drawings of same are needed to accompany the application.

    Attached is a copy of our by laws, but I suggest you check those in your area before doing the job.

    https://www.buffalocity.gov.za/folder.php?id=sSWeUsCZg


    Peace out ... Derek.
    I am in Cape Town but a direct customer of Eskom, would COCT by-laws still apply to me?

  9. #69
    Full Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    58
    Thanks
    18
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Derlyn View Post
    Tested a generator this morning. The specific model ...... Ryobi rg 6900K.

    Results as follows:

    No load ..... L - N 235V ; L - E 160V ; E-N 75V

    With load .... L - N 235V ; L - E 235V ; E-N 0V

    Is there anyone who can explain this. I'm wracking what's left of my brain cells but cannot understand it.

    Peace out .. Derek
    Best guess is the voltage regulator stuff and perhaps a form of induced EMF on the N and E etc. A generator needs to run on load as far as I understand to run correctly.

    I have been told if a generator is producing more than the load it does not like it as it has to keep revs up and not stall but then too much voltage applied etc.

    Anyway that's my best so far as to why seeing voltages like that. Also then when it's under load then the genny i believe is then not VoV which is great

    Sent from my SM-N960F using Tapatalk

  10. #70
    Gold Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    581
    Thanks
    32
    Thanked 66 Times in 64 Posts
    @Dylboy. Yes, not vov for sure. I've checked if vov then the voltage is split 50/50 whether there is a load or not.

    Also, I cannot see 3 thick leads coming from the stator. Only 2, live and neutral. On vov wound, there are 3 thick leads coming from the stator with one of them (centre tap ) connected to earth.

    Gonna do more tests on Monday.

    Gonna connect it to installation and see if earth leakage works as it should.

    Peace out .. Derek

Page 7 of 9 FirstFirst ... 56789 LastLast

Similar Threads

  1. 230 volt generator with a V-O-V earth connection
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 29-Jul-20, 09:33 AM
  2. gas stove connection
    By ians in forum General Chat Forum
    Replies: 3
    Last Post: 09-Feb-15, 11:44 AM
  3. New Electricity Connection
    By elaine25 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 27-Mar-14, 01:00 PM
  4. NETWORK CONNECTION PROBLEMS
    By Coolblue in forum Technology Forum
    Replies: 7
    Last Post: 07-Feb-13, 04:18 PM
  5. Internet connection speed
    By Martinco in forum Technology Forum
    Replies: 16
    Last Post: 11-Oct-12, 12:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •