    If I am not mistaken, this falls under alternative load Earth/Neutral bonding wiring.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  2. #82
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    One or 2 photos. ( man of my word )

    Click image for larger version. 

Name:	20211129_105719.jpg 
Views:	155 
Size:	44.2 KB 
ID:	8408

    Floating earth


    Click image for larger version. 

Name:	20211129_105822.jpg 
Views:	169 
Size:	40.5 KB 
ID:	8409

    With earthspike. 3 lights.



    Click image for larger version. 

Name:	20211129_112134.jpg 
Views:	197 
Size:	64.2 KB 
ID:	8410

    My earth/neutral bridge ( yellow lugs )



    Click image for larger version. 

Name:	20211129_113410.jpg 
Views:	151 
Size:	63.4 KB 
ID:	8411

    Testing in kitchen with genny.


    We modified 2 genny's today. The one was the Ryobi 6900 and the other was a Fragram 5 GFD-3 5kva.

    Tips. The wiring coming from the stator are not wired the same in these 2 models, so you need to make sure which one is being used for the neutral by removing the control panel in front.

    I will carry on checking different gennys, but it seems to me that anything 5kva or bigger is not vov, but one still needs to confirm.

    Peace out .. Derek

  3. Thanks given for this post:

    Dylboy (29-Nov-21)

  4. #83
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    That is great ! Thank you for the pics. Nice to learn a bit more on the genny side.

    Having a thought (can be dangerous when i have a thought haha)

    Instead of opening up the stator and doing what you have done , could it be possible to take the output of the genny and then bond the Neutral and the Earth to the earth spike ?

    Now there are the gennys that have the centre tap and some not so not sure if it will work for both.

    In my opinion it will work bar maybe the centre tap earth, but I would have to experiment unless a wise person on here knows.

    Why I am having this thought is just for warranty stuff as opening the stator may void warranties and all.

    Sent from my SM-N960F using Tapatalk

  5. #84
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Dylboy View Post
    That is great ! Thank you for the pics. Nice to learn a bit more on the genny side.

    Having a thought (can be dangerous when i have a thought haha)

    Instead of opening up the stator and doing what you have done , could it be possible to take the output of the genny and then bond the Neutral and the Earth to the earth spike ?

    Now there are the gennys that have the centre tap and some not so not sure if it will work for both.

    In my opinion it will work bar maybe the centre tap earth, but I would have to experiment unless a wise person on here knows.

    Why I am having this thought is just for warranty stuff as opening the stator may void warranties and all.

    Sent from my SM-N960F using Tapatalk
    Hello Brother

    Bridging the neutral and earth will work on a vov wound, BUT the centre tap must first be disconnected otherwise you are basically shorting out one half of the stator coil and the genny wont last long at all.

    Peace out ... Derek

  6. Thanks given for this post:

    Dylboy (29-Nov-21)

  7. #85
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by Derlyn View Post
    Hello Brother

    Bridging the neutral and earth will work on a vov wound, BUT the centre tap must first be disconnected otherwise you are basically shorting out one half on the stator coil and the genny wont last long at all.

    Peace out ... Derek
    Ah yes of course, Thank you !
    So in the end it would have to be opened anyway to verify. Either way really enjoyed this post.



    Sent from my SM-N960F using Tapatalk

  8. #86
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Dont need to open to confirm. Just run the genny and check voltages with meter. Vov will give 115 between neutral and earth and 115 between live and earth, a 50/50 split, then you know its vov.

    Peace out .. Derek.

  9. #87
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ah yes true to that too, that is the first test I would do anyway prior to opening. Either way the customer will be informed of what would need to happen and get permission if opening up is required.

    Sent from my SM-N960F using Tapatalk

  10. #88
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The solution is simple ... signage and awareness ... you cant do any more that that.

    I install the generator plug point at the meter use the correct equipment (correct size wiring ... circuit breakers ... changeover switch ... IP 65/7 enclosures and lable label and label) then attach a note to the email with the relevant information with regards to V-O-V ... max generator size for the applications and wait for my payment notice.
    Comments are based on opinion...not always facts....that's why people use an alias.

Page 9 of 9 FirstFirst ... 789

Similar Threads

  1. 230 volt generator with a V-O-V earth connection
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 29-Jul-20, 09:33 AM
  2. gas stove connection
    By ians in forum General Chat Forum
    Replies: 3
    Last Post: 09-Feb-15, 11:44 AM
  3. New Electricity Connection
    By elaine25 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 27-Mar-14, 01:00 PM
  4. NETWORK CONNECTION PROBLEMS
    By Coolblue in forum Technology Forum
    Replies: 7
    Last Post: 07-Feb-13, 04:18 PM
  5. Internet connection speed
    By Martinco in forum Technology Forum
    Replies: 16
    Last Post: 11-Oct-12, 12:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •