Thread: Neutral leaking 220V to Earth

  1. #1
    New Member
    Join Date
    Sep 2014
    Location
    Bloemfontein
    Posts
    2
    Thanks
    0
    Thanked 1 Time in 1 Post

    Cool Neutral leaking 220V to Earth

    Hi

    I've recently been doing contracting work for a factory, mostly upgrading and alterations to the electrical system of the factory, in order to meet with compliance for the COC's. While I'm busy doing that the customer requested from me to go and check a problem they're experiencing in their packaging area (which I was still yet to start fixing in the near future).

    They've reported to me that when they use their single phase 220V vacuum sealing and normal sealing machines, that the power lights dim out on their machine, as soon as they start using the sealing elements. I took the machines to a different location, in the factory, and they work 100%.

    I've started looking at the plug socket's and the DB itself for loose connections etc. And find nothing wrong, when doing standard voltage + resistance tests. I've also went and fetched anything that could use (eg a heat gun with different heat settings), started plugging it in a different socket outlets. The heat gun works fine under normal circumstances (as tested at the workshop). I plug it in and use the different heat settings. The first two only blows the fan, but you cant feel any heat coming out. The third and fourth settings plainly doesn't go on at all.

    Ive plugged in my tester, and asked somebody just to operate the heat gun, I've found that the single phase live 220V to ground goes dead (0V) and the neutral to ground 220V. Switching off the heat gun shows again the normal readings live to neutral is 220V, live to ground 220V, and the neutral to ground (earth) 19V.

    I got two questions, does the elevated neutral to earth voltage seem too high (I tested the upstream DB, found that the Neutral - Earth is 110mV)? And then did anybody experience this as yet?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yes, the N-E voltage is too high, it's 220v under load which is way too high, even 19v is too high!!!

    Just be careful with what tester you use though, many digital testers can give confusing readings because of their high input resistance makng them super-sensitive to 'ghost', 'stray' or coupled voltages but this is often more of an issue with dead tests so it could go some way to explaining the 19v you see with no load connected. See here for more info.

    If the neutral voltage with respect to earth is rising when the circuit is under load it's almost certain the neutral is high resistance somewhere in the circuit. Most likely cause is a poor or burned connection or termination. The other possibility is the the CPC is rising in voltage WRT true earth and the neutral is staying at 0V, this is an even worse case scenario and could injure or even kill someone who comes into contact with the chassis or anything connected to the earth wire. Either way this is a fault you're going to have to localise and repair and the circuit in question is hazardous and should be isolated and locked out until remedial work is complete. A loop impedance tester would be the weapon of choice rather than a heat gun and a volt meter.
    _______________________________________________

    _______________________________________________

  3. Thanks given for this post:

    DieterT (20-Oct-14)

  4. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The fact that live to earth goes to 0 volts indicates the earth is broken or disconnected in the circuit or incorrectly wired. Take an earth leakage plug tester and plug it into the socket and check if all 3 lights come on then try trip the earth leakage unit. Chances are the plug tester will show you were in the circuit the problem is.

  5. #4
    New Member
    Join Date
    Sep 2014
    Location
    Bloemfontein
    Posts
    2
    Thanks
    0
    Thanked 1 Time in 1 Post
    Ok I've located the problems (and quite a lot of them). I've located a connection box, on top a cable racking system on the way from the sub station, to the particular DB in question. The neutral connection done there was crimped, but not properly. Rectified the problem.

    I've took out all the connected loads, out of all the plugs located in the area, switched off all the breakers, EL's and the main breaker, done a insulation test, found a few dead shorts, some by incorrect cable cleaning methods, and some by poor connections on top on the rooftop. I've even had to remove an entire circuit (cable and all), of all the damage done, because of people used that are not even qualified electricians. I have to replace the entire cable, plugs etc on that line, but that is a story for another day.

    I've even found one Earth Leakge by itself, getting a reading of 0,3 meg ohm tested on 500V, between live and neutral, without cables on it, and in switched off position. Replaced that one.

    When done with all that, I've checked the system again, everything tested now was correct. Also that loose main neutral, test now correctly to earth, as from the main sub station.

    Strange how incorrectly done bonding of cables, can make a electrician's life so difficult. Especially on a neutral line.

    It is as AndyD stated, this could have been a hazardous situation, which no one was even aware off, but as with most of normal production factories in South Africa, companies tend to place safety dead last, and production first. Using correct and qualified electricians instead of normal assistants working in the factory, would make all our lives a lot easier.

    Thanks for the info.

  6. Thanks given for this post:

    DieterT (20-Oct-14)

  7. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Glad you got it sorted out, the circuit was undoubtedly a hazard. Most of the time with these types of faults you just need to follow the entire circuit and a visual inspection of all terminations will reveal the problem although it's sometimes logistically easier said than done though in a working factory environment.
    _______________________________________________

    _______________________________________________

  8. #6
    Junior Member
    Join Date
    Jan 2014
    Location
    Newcastle
    Posts
    14
    Thanks
    13
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by ians View Post
    The fact that live to earth goes to 0 volts indicates the earth is broken or disconnected in the circuit or incorrectly wired. Take an earth leakage plug tester and plug it into the socket and check if all 3 lights come on then try trip the earth leakage unit. Chances are the plug tester will show you were in the circuit the problem is.
    I think that's what I would have done first before resorting to earth loop impedance tester. Either way both should lead to an idea of what seems to be F*** Up.

  9. #7
    Full Member
    Join Date
    Feb 2012
    Location
    Cape Town
    Posts
    41
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Needing some help with a very strange problem. Using a 220V single phase spinning disc KWH meter I measure 220V N-E with the load on (NOT A GOOD THING).
    Load Off 0V N-E. Change KWH meter to a DIGITAL KWH meter and measure 0V N-E with load - Fixed! However when I change back to a NEW spinning disc KWH meter the problem re-occurrs. Can anyone explain why the spinning disc "creates" this problem. I have done an insulation resistance test which comes up clean. All the connections are tight and free of debris. No joints in the SWA cable. Really confusing...

  10. #8
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Maybe I am going to ask a few stupid questions.
    Where did you do the voltage measurement, before or after the meter?
    What was the reading between Live and Earth, with reference to the Neutral earth measurement?
    It could be the instrument is incorrectly labelled on the output side or the input side (take your pick), so Neutral is where live is and Live is where Neutral is.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  11. #9
    Bronze Member
    Join Date
    Oct 2014
    Location
    Pretoria
    Posts
    126
    Thanks
    16
    Thanked 16 Times in 15 Posts
    Possibly the star point on transformer that is not properly earth or earth been stolen that supplies the factory.
    Do an earth loop impedance test at your main DB and see if he earth resistance is above 1.92ohm
    If you find the resistance to be to high, then bridge out the neutral and earth at the supplier meter box.
    Should elevated voltage on neutral exceed 25v then inform the supplier, should it exceed 50v then disconnect the installation and inform the supplier

  12. #10
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by DieterT View Post
    If you find the resistance to be to high, then bridge out the neutral and earth at the supplier meter box.
    I get the distinct sense that is advice that needs some rather long "subject to" clauses.

Page 1 of 2 12 LastLast

Similar Threads

  1. Installation of 220V downlights
    By Oblivious in forum Electrical Contracting Industry Forum
    Replies: 105
    Last Post: 14-Feb-20, 09:57 AM
  2. Solar system and Eskom supply, (a Neutral Question)
    By Tinman in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Jul-15, 09:35 AM
  3. 12V fitting with 220V lamps
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 34
    Last Post: 14-Feb-14, 01:59 PM
  4. 220v Downlight DIY Installation
    By daveob in forum Electrical Contracting Industry Forum
    Replies: 42
    Last Post: 24-Jan-13, 07:21 AM
  5. 3 core cable running 2 phases and neutral is OK?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 09-Jan-12, 07:44 AM