    Testing live installation

    Ok how to upset everyone.

    A client wants a COC on an installation that cannot be switched off. Discuss....

    I said to the client it can't be tested effectively. Yes, you can do earth test (fly lead method) when live. Insulation resistance... No chance. Polarity, yes. Make and break check, nope. Earth leakage (I don't there are any). Voltage off load, not possible.

    I accept there are things that cannot be turned off. What do you guys think....

    I do a lot of shop work in malls and, no the mall will not let you shut down the entire mall so you can do a no load voltage test.

    This job isn't a shopping centre and i understand it can't be turned off. The consequences would be quite dire. What can you do in these situations.

    Just curious. I know most will say "won't touch with a barge pole"

  2. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    wont touch with a barge pole

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    I always ask - what do you do when there's a power failure? That tends to take the wind out of their sails most times. Even where there are backup generators, there's still a point where the power goes down before the standby power kicks in.

    You just have to stand firm. The power needs to go off at some point. At least this will be a planned outage.

    We've had to work around some pretty crazy hours for the outages at some instances, but haven't had one yet where they actually, genuinely, and absolutely could not make a plan.

    And yes, that does include some shopping centres - with backup generators to boot. And high end IT installs on UPS. And 24/7 manufacturing plants.

    You want a COC - the power will be going off at some point. Make a plan.

    Quote Originally Posted by skatingsparks View Post
    I do a lot of shop work in malls and, no the mall will not let you shut down the entire mall so you can do a no load voltage test.
    Probably worth pointing out that if the mall is the only point of consumption on the transformer, you can't shut down absolutely everything on the load side of a transformer anyway. On some of the heavier supplies, some of your readings are going to have to be calculated anyway.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The IR of the installation at 220v can be calculated by measuring global installation leakage whilst live.

    We've actually issued two CoC's in the past decade on critical installations in conjunction with the area electrical inspector. You could try liase with him but if it's just a corporate convenience thing I doubt he'll entertain the required test exemptions.

    You say you don't think there's any RCD's, I'm interested to know what the installation is...
    _______________________________________________

    _______________________________________________

  5. #5
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Its the power to control panels of a baggage handling system at an international airport. Everything is interlinked so if one part goes down the whole system shuts down (ie the whole airport baggage handling system gets weird from check in to baggage collection). I'm seeing the baggage handling system as a (very big) appliance. I mean everything that runs on the system is from one of about 36 panels (that I know of not all of which are required to be tested) which are interlinked by profibus signal cables so they can talk to each other. I think anything connected to the control panel is part of the fixed appliance.

    Shutting a mall down, inconvenient, shutting an international airport baggage handling system down... er no.

    I worked on the system during the install when it was being upgraded for the world cup in 2010 but I was working for a company then. Another company put the power to the panels and I was doing the power from the panels to the motors and control cables for the e-stops etc.

    What do you think?

  6. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yeah, as you say anything fed from a control panel isn't part of the electrical installation for CoC purposes, only the main power distribution DB's and sub DB's plus the final circuits to the point of isolation.

    Is there a back-up power solution ie generator/UPS etc connected to the baggage handling system? If there is it makes your life fairly easy. Back-up power would also be a double-edged sword because if there isn't any then it's going to be kinda difficult to motivate it as a critical system and get it considered for any special treatment or exemptions.

    TBH if the rest of the installation is compliant plus there's no socket circuits then I would seriously consider just issuing the CoC with a calculated IR result and leave out any off-load voltage results you can't obtain and include your reasons in the notes section.
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    skatingsparks (10-Jul-14)

  8. #7
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Thanks Andy. I'm going to do a site visit just have look, see if its feasible to pretty much what you suggested. I'll make clear to client, they who won't allow us to switch off, the limitations of what we are doing and I figure if I cover all those limitations in the notes section I think it will be OK. Going to have proper look first before deciding. Its just ones of those kind of jobs that could lead to the big jobs which would take the business to the next level but I'm not going to sign off something that will give sleepless nights. I'm a bit OCD when it comes to COC's

  9. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    Testing live installation

    A fluke 1653b, 435, mA meter and a ti 25 problem solved. You can collect all the readings and some and have recordings so that you can join the CYA club 😉 no need to be OCD. I believe the most import part of an COC or any electrical installation for that matter is the earth. Hence the reason i own and use a mA clamp meter, it tells you all sorts of info and with a basic understanding of ohms law many readings can be calculated from other tests. Something to think about.
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #9
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    So the panels had UPS inside just to keep the PLC's powered up in the event of a power failure giving time for the generator to kick in. The whole system is just one big lump of earthed metal. The conveyers are metal standing on metal mesh floor all interlinked with steel work. The panels often stood in groups running different lines. Each panel was individually fed with its own SWA and separate earth wire. The earth reading were pretty much always 0.01 ohms using a fly lead from a local main panel (fed from a substation). The local main switch had its kA rating on it so that was noted as the kA rating (from supplier). The MCB's inside the panels were rated at 35kA(!). The supply cables were mostly massively over sized for the expected load. We did ins res from the local mains to the panels where it was possible to isolate and stated a limitation on what we were not permitted to turn off. The testing was done less that 5 years ago. For voltage on load and off load we measured when the machine conveyors were not running and again when they were running (meaning the load was the power to the PLC and the cabinet light and fan which is barely 1 amp when not running and worst case scenario when it is running).
    All reading were good. The only things we could find were no glands on the earth cables coming into some panels, the earth cable were coloured black (which are now been marked with green and yellow earth tape or heat shrink inside the panel and where it enter the panels), one over size breaker on a 2.5 surfix cable (40 amp) and one real mess where a panel was drawing 180 amps through a 160 amp isolator when the machine was running. Taking the new thermal imaging camera down there tomorrow see if that picks up anything else.

    That's the best I can do in the circumstances.

  11. Thanks given for this post:

    AndyD (23-Jul-14)

  12. #10
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by skatingsparks View Post
    The local main switch had its kA rating on it so that was noted as the kA rating (from supplier). The MCB's inside the panels were rated at 35kA(!). The supply cables were mostly massively over sized for the expected load.
    I handed out my copy of the SANS code to a new employee the other day, and I've still got to replace it. So I can't reference the specific section. But look up the section on PSC, particularly on how to calculate PSC.

    Yeah - the kA rating might seem high, but don't assume what's in there now is enough. We've had installations that have needed 200kA ratings at the main switch where there was "only" a 50kA rated switch in place.
    One might expect that someone did it right with the original installation, but CYA and do the calculation anyway. (If you haven't already).

    You'll need the transformer's internal resistance rating from the plate on the transformer, + the size and length of the main supply cable.

Page 1 of 2 12 LastLast

Similar Threads

  1. Live entertainment in Durban
    By MGM in forum General Chat Forum
    Replies: 0
    Last Post: 05-Feb-13, 07:49 PM
  2. Testing an exisitng installation without power
    By ians in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-12, 09:43 PM
  3. Testing an installation with more than 5 installations
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 03-Sep-12, 07:45 PM
  4. games for windows : Live
    By twinscythe12332 in forum Technology Forum
    Replies: 7
    Last Post: 30-Jun-10, 11:05 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •