    Quote Originally Posted by Sparks View Post
    Keep looking, if I find the time i will get it. Main switches must isolate all Live as well as the Neutral. In a single phase installation that means double pole: SP+N, Isolator or ELCB can serve as main switch, whichever is used must be indicated on the COC as well. You may have a SP CB before the main switch often the case when the ELCB is the main switch. For a 3ph supply, surprising to almost all, you are supposed to use a 3ph 4pole isolator, 3pole+N or 3phELCB. It is in the regs but i am afraid I do not know exactly where. If I get a chance I will look for you. A sub DB may be fed from a SPCB but the DB must have a DP as main switch which is also specified in the regs.
    In a single phase system you may have a combination of a circuit breaker and an earth leakage instead of an earth leakage with integrated overload protection.
    However where this earth leakage is used as the isolating device for the db then it must also isolate power to the accompanying circuit breaker which will then be mounted on the load side of the earth leakage.
    Should you wish to remove various circuits from the earth leakage circuit then an additional isolating device must be installed before the earth leakage.
    At this point the accompanying circuit breaker may be installed on the supply side or the load side of the earth leakage.

    See SANS 10142-1:2009 6.8.1
    6.8.1 Circuit-breakers used as main or local switch-disconnectors, A circuit-breaker that is used as a main or local switch-disconnector (see
    6.9.4) shall comply with the relevant requirements of a standard given in clause 4 for switch-disconnectors, or, alternatively, a switch-disconnector
    shall be positioned on the supply side of the circuit-breaker.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  2. #12
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    In the case of a single phase circuit I would use a SP+N as the main isolator and then install a ELCB omitting to connect the the lighting circuits on the ELCB for safety.Then again the difference between domestic and industrial D.B.s need to be considered.Using an ELCB as a main switch I have had whole production lines come to a standstill through nuisance tripping (night watchmans kettle)

  3. #13
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think you have a very valid point. I consider any installation, even domestic, that uses a single RCD as a main switch to be poorly designed. The nuisance factor is far too high if there's ever a leakage fault. I don't understand why it's still the norm nowadays when you can purchase a half decent RCD for afew hundred bucks so splitting the load between 2 or 3 RCD's wouldn't break the bank.

    On several jobs recently we've had a specification for RCBO's on every circuit. I had to import them myself because nobody within a thousand Km stocks them. They've been using these in many countries for several years now but every wholesaler I spoke to hasn't even heard of them.

    Click image for larger version. 

Name:	RCBO.jpg 
Views:	382 
Size:	9.0 KB 
ID:	4444
    _______________________________________________

    _______________________________________________

  4. Thanks given for this post:

    ians (05-Mar-14)

  5. #14
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by AndyD View Post
    I think you have a very valid point. I consider any installation, even domestic, that uses a single RCD as a main switch to be poorly designed. The nuisance factor is far too high if there's ever a leakage fault. I don't understand why it's still the norm nowadays when you can purchase a half decent RCD for afew hundred bucks so splitting the load between 2 or 3 RCD's wouldn't break the bank.

    On several jobs recently we've had a specification for RCBO's on every circuit. I had to import them myself because nobody within a thousand Km stocks them. They've been using these in many countries for several years now but every wholesaler I spoke to hasn't even heard of them.

    Click image for larger version. 

Name:	RCBO.jpg 
Views:	382 
Size:	9.0 KB 
ID:	4444
    Unfortunately I cannot make much out as the picture is extremely small.
    Is it possible to post a larger version?
    What is that above the circuit breakers?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  6. #15
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    This would confuse the local sparkies. I assume this is a pic of a DB used in the USA not in SA by the colour code. Black live and blue neutral with an exposed bussbar at the bottom. My kind of DB nice and neat.

  7. #16
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Slow Blow View Post
    Does the main switch on a single phase DB have to be single pole, single pole and neutral or double pole, I ask this as there seem to be some confusion amongst a lot of local electrical CoC providers in Cape Town.
    The db must be protected by a double pole disconnecting device that disconnects both the live and neutral.
    If there is no integrated overload protection in the disconnecting device then a circuit breaker may be installed on the load side of the disconnecting device.
    See SANS 10142-1:2009 section 6.9
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #17
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Leecatt View Post
    ........What is that above the circuit breakers?
    Quote Originally Posted by ians View Post
    This would confuse the local sparkies. I assume this is a pic of a DB used in the USA not in SA.......
    It was just a picture showing RCBO'S for the benefit of anyone uncertain what they are. t's not my handywork (my panels are far neater than that ) the DB shown is actually a UK 17th Edition compliant one, each socket and light circuit MCB has two wires because they generally use 32A ring circuits.

    RCBO

    Name:  111.jpg
Views: 1188
Size:  4.7 KB
    _______________________________________________

    _______________________________________________

  9. #18
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,660
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    A residual-current circuit breaker with overload protection (RCBO) combines the functions of overcurrent protection and leakage detection.
    With thanks to Wikipedia.

  10. Thanks given for this post:

    Mark_Spark (26-Jun-16)

  11. #19
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Thanks Dave, forgot about wikipedia momentarily. Basically they're the size of an MCB, well at least the more recent versions are, the older ones are quite a bit taller than an MCB but same width. You fit one for each circuit being supplied from the DB and they provide earth leakage protection as well as overload protection to each individual circuit. The bonus is that an earth leakage fault just causes tripping of the guilty circuit and not the entire premises.
    _______________________________________________

    _______________________________________________

  12. Thanks given for this post:

    Mark_Spark (26-Jun-16)

  13. #20
    Full Member
    Join Date
    Feb 2014
    Location
    Fish Hoek
    Posts
    55
    Thanks
    6
    Thanked 3 Times in 3 Posts
    I have learned something new now, I have been using RCD's for years and always thought that they were expensive ELCB's
    Apparently there is nothing that cannot happen today.

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Replies: 2
    Last Post: 25-Apr-12, 10:15 AM
  2. main agreement or basic conditions of employment act
    By melvinbrucepaton in forum Labour Relations and Legislation Forum
    Replies: 1
    Last Post: 10-Feb-12, 08:44 PM
  3. Generator starts while the main power is on
    By jvan66 in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 12-Oct-11, 01:42 PM
  4. Main Switch?
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 08-Feb-11, 10:16 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •