In a single phase system you may have a combination of a circuit breaker and an earth leakage instead of an earth leakage with integrated overload protection.
However where this earth leakage is used as the isolating device for the db then it must also isolate power to the accompanying circuit breaker which will then be mounted on the load side of the earth leakage.
Should you wish to remove various circuits from the earth leakage circuit then an additional isolating device must be installed before the earth leakage.
At this point the accompanying circuit breaker may be installed on the supply side or the load side of the earth leakage.
See SANS 10142-1:2009 6.8.1
6.8.1 Circuit-breakers used as main or local switch-disconnectors, A circuit-breaker that is used as a main or local switch-disconnector (see
6.9.4) shall comply with the relevant requirements of a standard given in clause 4 for switch-disconnectors, or, alternatively, a switch-disconnector
shall be positioned on the supply side of the circuit-breaker.