    Circuit Breaker tester

    What puzzles me, we have to do so many tests on an installation, and one of the most important tests that should be taken into account is a circuit breaker that trips at its rating.
    Otherwise whats the point.
    Some breakers seem to buzz, some just trip, some just get hot.....i feel strongly about this as this is a protection device.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Testing circuit breakers is a straight forward operation but you need a primary current injection unit which will set you back about 350 thousand Rands plus shipping and import duties so it's only worth the investment if yu're setting it up as a primary business.

    I suppose you could check up to 20A with a bench rig and check their disconnect times at 2 or 3 x their rating In value).

    Circuit breakers tend to buzz when the load is highly inductive (AC3) or poor power factor/high harmonics. They run warm when they're loaded close to their rated value because of the internal thermal element assuming it's not poor terminations, all this would be normal behaviour.

    The biggest causes of circuit breaker failure we come across (excluding the cheap rubbish that's obviously poorly manufactured) are poor terminations, debris inside the breaker (usually where some low-life has drilled above the panel or DB and not covered it) and excessive wear and tear usually when the customer is using the breaker frequently as an isolator. The damage from the first two would usually be obvious without complicated testing.
    _______________________________________________

    _______________________________________________

  3. Thank given for this post:

    Dave A (22-Dec-13), ELECT 1 (21-Dec-13)

Similar Threads

  1. Is no service a contract breaker?
    By insulin in forum Marketing Forum
    Replies: 7
    Last Post: 10-Mar-14, 06:21 PM
  2. which tester
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 19-Jul-11, 11:03 AM
  3. Best Place To Buy A Tester
    By SparkyScott in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 24-Apr-11, 08:59 PM
  4. buzzzing circuit breaker
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 08-Mar-11, 10:47 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •