Page 1 of 2 12 LastLast
Results 1 to 10 of 14

Thread: Earth Leakage

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Earth Leakage

    Is an earth leakage faulty if it trips before or after the mA rating stipulated on the earth leakage?

  2. #2
    New Member
    Join Date
    Apr 2013
    Location
    South Africa
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I had this discussion with my electrician this morning. In my opinion it is definitely faulty if it trips after, as anything over 100 milliamps becomes lethal. It can also be faulty if it is too sensitive and trips around the 20 milliamps range, however not lethal, I think, it trips too quick and needs to be replaced. Any electricians out there that can shed some more light on this?

  3. #3
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Talmadge View Post
    I had this discussion with my electrician this morning. In my opinion it is definitely faulty if it trips after, as anything over 100 milliamps becomes lethal. It can also be faulty if it is too sensitive and trips around the 20 milliamps range, however not lethal, I think, it trips too quick and needs to be replaced. Any electricians out there that can shed some more light on this?
    I had this problem last week, earth leakage and random tripping.
    I tested the unit with no load connected and found it was very sensitive and tripped at 21 Milli-amps.
    I found another unit that trips at 25 Milli-amps and the problem has gone now.
    By the way the acceptable range for any earth leakage unit is between 50% and 100% of its rating as indicated on the unit.
    For a modern home that would be between 15 and 30 Milli-amps
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i think in sans it says 20 -30ma is acceptable. i need to go back and check.

  5. #5
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    See
    8.7.12 Operation of earth leakage units
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    If the stove is connected to an isolator, there is no need to connect it to earth leakage (we don't use stove couplers in Durban) The only time you have to connect it to earth leakage is when the isolator has a combo isolator socket outlet, like we had in the old days.

  7. #7
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Yes it is acceptable but would if the manufacturer standards stipulates 20mA on it, it must trip on that rating. But what if it doesn't. Even if it's a new earth leakage. Where is the fault?

  8. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Andy if anything I do believe in this country, I could see less being connected to the earth leakage rather than more earth leakage units being installed

  9. #9
    New Member
    Join Date
    Apr 2013
    Location
    South Africa
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Is it tripping before or after?

  10. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The earth leakage is faulty if it doesn't trip after 30 Ma or if it trips when all the wiring is disconnected.

Page 1 of 2 12 LastLast

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. Earth leakage trips at night??
    By Jongseun in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 18-Jun-12, 10:47 PM
  4. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •