    bathroom light and aircon cord

    Should a light with an IP rating of 20 be allowed to be installed in a bathroom where there is a shower. Horizontally it's within 600mm but vertically it's higher then 2,4meter? Is it okay to have the cord that comes with the aircon plastered in the wall and just enough slack left for it to be plugedinto the plug?

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Pieter00 View Post
    Should a light with an IP rating of 20 be allowed to be installed in a bathroom where there is a shower. Horizontally it's within 600mm but vertically it's higher then 2,4meter?
    You don't specify 600mm from what?

    If it is within 600mm from the edge of the shower tub, but external to zone 1, then it may have fallen into zone 2. However zone 2 only reaches 2.25 meters from the ground therefore it is in zone 3
    If, however, it is within 600mm from the shower rose then it is in zone 1 as zone 1 reaches 2.5 meters from the floor.

    I am assuming zone 1.
    You may not install the light for the following reasons.
    1. Any electrical equipment has to be IPX5

    I am assuming zone 3.
    You may not install the light for the following reasons.
    1. Any electrical equipment has to be IP21


    Quote Originally Posted by Pieter00 View Post
    Is it okay to have the cord that comes with the aircon plastered in the wall and just enough slack left for it to be plugedinto the plug?
    How long is the cable?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    About 1m that they plastered

  4. #4
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Pieter00 View Post
    About 1m that they plastered
    PVC insulated cables may be buried into plaster. I don't know what insulation there is on flexible cords but I imagine it is PVC.
    The cable is less than 1.5 meters in length and therefore is allowed as per 6.16.1.11. and does not form part of the electrical installation
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

Similar Threads

  1. Bathroom heater installation
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Jun-12, 06:49 AM
  2. Light fixtures in a new bathroom
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 13-Apr-12, 11:11 PM
  3. Socket outlet in bathroom
    By mlpotgieter in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Oct-11, 12:10 AM
  4. CUTTING THE CORD
    By Graeme in forum General Business Forum
    Replies: 2
    Last Post: 23-May-07, 12:49 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •