    Two Phase Installation system???

    I was just reading through SANS 10142, and under annex P, Authority for issuing a test report and a Certificate of Compliance.
    Which is installation is Two-phase, is it two phases from three phase system?

    Any one to assist

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yes, a two-phase system consists of 2 live phases, one neutral and an earth, as you say it's basically a 3-phase system that's missing one phase. It's not very often you see a 2-phase installation nowadays, I've come across only one in the last 15 years or so. Maybe they're more common in certain areas, I'm not sure TBH.
    _______________________________________________

    _______________________________________________

  3. #3
    Junior Member
    Join Date
    May 2012
    Location
    Windhoek
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you very much AndyD,

    Am a bit confused here regarding Voltage drop calculation,

    Click image for larger version. 

Name:	Voltage drop calculations.jpg 
Views:	308 
Size:	22.8 KB 
ID:	3401
    E.1.4 Circuit DB/C
    Selected cable voltage drop to be repeated for each load point from the
    previous load point. Amdt 5
    From table 6.4(b) (voltage drop), for a 16 mm2 two-core cable single-phase a.c., the voltage drop is 2,8 mV/A/m

    DB to C1 voltage drop = (2,8 x 10-3) x (5 x 15) x 10 = 2,10 V Amdt 5
    C1 to C2 voltage drop = (2,8 x 10-3) x (4 x 15) x 8 = 1,34 V Amdt 5
    C2 to C3 voltage drop = (2,8 x 10-3) x (3 x 15) x 8 = 1,01 V Amdt 5
    C3 to C4 voltage drop = (2,8 x 10-3) x (2 x 15) x 6 = 0,50 V Amdt 5
    C4 to C5 voltage drop = (2,8 x 10-3) x (1 x 15) x 9 = 0,38 V Amdt 5
    Total voltage drop DB to C5 (red phase) = 5,33 V [1] Amdt 5

    My question is: why should they multiple the current by 5 at C1, by 4 at C2, by 3 at C3, by 2 at C4 and by 1 and C5.

    is this really right?

    My total voltage drop is 1.722V
    Last edited by Dave A; 14-Mar-13 at 08:25 PM. Reason: formatted superscript in formula

  4. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by Smut View Post
    My question is: why should they multiple the current by 5 at C1, by 4 at C2, by 3 at C3, by 2 at C4 and by 1 and C5.
    Point C1 is carrying 5 x 15A draw points, 1 at C1 and another 4 further down the line.
    Similarly C2 is carrying 4 x 15A draw points.

    From a "follow the logic" point of view, it might have been better if they started the point numbering from the furtherest point and worked back towards the supply point for these sorts of schematics. Of course from a signage point of view (if you were actually physically labelling each point) it makes more sense to number from point of supply...

  5. Thanks given for this post:

    Smut (14-Mar-13)

  6. #5
    Junior Member
    Join Date
    May 2012
    Location
    Windhoek
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thanks Dave,

    I really washed my brain.

  7. #6
    Email problem
    Join Date
    Dec 2011
    Location
    Evander
    Posts
    6
    Thanks
    0
    Thanked 1 Time in 1 Post
    Can the neutral be regarded as a live phase?

  8. #7
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    it is regarded as a live conductor according to 10142. its not a live phase,otherwise 2 phases and neutral would be 3 phase.

Similar Threads

  1. [Question] Three phase / Single phase
    By Martinco in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 14-May-12, 10:57 PM
  2. 3 Phase or 1 Phase.
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 10-Nov-10, 07:40 AM
  3. [Question] Phase rotation and PSC
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 06-Sep-10, 12:25 PM
  4. New demerit system-New driving points system hits the road
    By Candy Bouwer in forum General Business Forum
    Replies: 22
    Last Post: 23-Jul-09, 06:51 PM
  5. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •