    Earth loop impedance testing

    A question for all the bright sparks, It you are busy doing an inspection report and find the earth loop impedance reading higher than it should be, what do you do?

    I was told by the technical division of the Durban electricity department 2 very interesting points:

    1/ That i am suppose to do an earth loop impedance test at each and every plug socket or power outlet, interesting because according to page 276...8.7.5 Earht loop impedance test should be done at the the main switch.

    2/ If the reading is higher than it is suppose to be, for example 10 ohms at a 60 amp breaker, it is my responsibility to isolate the power imediately, report it to the electricity department and they will sort out the issue within the same day, funny they should say that because if i have switched off the power in the most recent test (15/11/2012) the power would still be off, i still havent had a reply from them todate. If i dont switch off the power i will be held responsible for any injuries caused by bad earth, surely the responsibilty would become theirs, if they dont attend to the problem within a 24 hour period?

  2. Thanks given for this post:

    mikep (07-Jan-15)

  3. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    What earthing arrangement did the premises have? TNCS?

    We perform an external earth fault loop impedance test (Ze) on the incoming supply with the earth disconnected and the installation isolated plus we do earth fault loop impedance testing (Zs) from the farthest end of any circuits we install to ensure MCB protection times are met.
    _______________________________________________

    _______________________________________________

  4. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Durban has a TN-S earthing system.

    I use a fluke 1653, so i can and do tests at every single point,

    voltage : L-N, L-E, N-E and include the phases if it is a 3 phase system.
    polarity.
    E/L (RCD as Andy refers to them) trip time which should be done in both in 0 and 180 degree (not a requirement in South africa) you can just use a normal plug in e/l tester.
    E/L tripping current.
    loop/line impedance and at the same time the prospective earth fault current.

    It gets a little more complicated when we test points in other applications like hospital theatres for example.

    The tests above are normally only done if the power is already on, for example in exsisiting installation inspection reports when properties are sold.


    What does the law(SANS) say about it, at what point should the loop impedance be carried out.

    What would be the ruling in court if someone was injured if you didnt switch off the installation?

    Just like elevated voltage rule, which happened a couple of weeks ago, i was called out on a Sunday morning to find the that the voltage was way about recommended value, so i didnt even think twice, I isolated the entire installation and boy did i collect for that. Customers where complaining threatning me win court cases etc, i eventually found the neutral bussbar between the transformer and the main frame had been stolen, i only reset the breakers at 4 pm. Lucky for me non of shop owners went through with the threats to sue me.
    Last edited by ians; 16-Feb-13 at 10:39 AM.

  5. #4
    Full Member
    Join Date
    Jan 2011
    Location
    midvaal
    Posts
    32
    Thanks
    3
    Thanked 0 Times in 0 Posts
    SANS 0142 section 8.7.5.2 tells you to install an ELU
    Eric

  6. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Looking at the COC as a whole you will see it is split into sections. The Loop,PSC, Supply Voltage,Elevated voltage,erath resistance are all tests done at the DB with the installation isolated. This is to determine whether the supplier is providing withing spec. Once these specs have been met the installation can be connected provided the installation complies. There are specs regarding bonding conductors, earth continuity which are tested for at each point of consumption will determine if the installation conforms to minimum requirements.

  7. #6
    Email problem
    Join Date
    Aug 2013
    Location
    Irene
    Posts
    1
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Did you ever resolve this with the municipality. I've just done an inspection and test on a very old property and it has an Earth loop impedance (at the main switch) of 16 Ohms! Way too high to allow 2 times the current to trip the 60A mains breaker. Most houses I've tested in the suburb have Earth loop impedances of less than 0.2 Ohms. All are TN-C-S by the way. One interesting thing is that the house has a Zellweger Uster ZE-22 ripple meter installed. I've tried to find a contact at Tswane Metro to see if they are still using these and if it could be introducing extra impedance into the circuit but to no avail. Also can I disconnect the thing? I'm probably going to be doing a complete rewire of the property as it dates to 1937 but the Earth loop problem is really a supplier problem. Early days though!

  8. #7
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    I see my previous response has the spelling of a new SA graduate, my apologies. I however reiterate what I said. Do the test at the main switch with it off. The ripple relay will not influence the reading at all. What must be tested at all the points of consumption for the COC is the earth continuity to the DB. This must comply with the regs according to the CB rating of the particular circuit. The local supplier is obligated to rectify a non-compliant loop impedance reading immediately. If you cannot get hold of a local supply employee willing to lift his backside you can resort to threats of claims for damages and the possible charges of culpable homicide being laid against said authority as well as public denounciation in the interest of consumer safety as well as fraudulent abuse of monopoly.

  9. Thank given for this post:

    Dave A (10-Apr-14), GrahamF (10-Apr-14)

  10. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Some feedback...it is 2019 ...still havent heard from the electricity department.

    I now have another 16 ohm reading...reported it and logged the fault report number on the COC...what more can we do?

  11. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by ians View Post
    reported it and logged the fault report number on the COC...what more can we do?
    We don't issue the COC until the earth loop impedance fault is fixed.
    And we nag.

  12. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dave A View Post
    We don't issue the COC until the earth loop impedance fault is fixed.
    And we nag.
    it is 2019 and we have to sit and listen to everything being repeated in 10 official languages then press 1 or 2 or 3 etc etc etc

    is there not an email or whattsapp message service ...where you can report a fault and they can get back to you at some stage?

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Loop Impedance
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 20-Jan-21, 03:00 PM
  2. Earth loop impedance and prospective short circuit (PSC)
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 21-Jan-16, 04:10 PM
  3. The value of split-testing
    By Norri in forum Marketing Forum
    Replies: 5
    Last Post: 22-Jun-12, 02:18 PM
  4. Testing with a neon
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 26-Feb-11, 11:46 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •