    3 Phase Voltage Problem

    Got a problem with a 3 phase voltage machine using 2 compressors for heating. When the isolator is in the open position - that is off :-) I get the normal phase to phase voltage of 400V. As soon as I switch the isolator on the machine's phase failure prevents the machine from turning on as the voltage is not the same across the phases. When I measure I get 500 on one then 270 on another. These are really weird voltages I'm getting. I have swapped the phase conductors around which did not help. Could the phase failure be faulty? Any help would be awesome!

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    If you're getting 500v across 2 of the phases and only 270 across another two then it sounds like you're missing a phase.

    Test from each phase to an earth at the supply side of the isolator with it in the off position you should get 220-230volts. Disconnect the load and repeat the test on the load side of the isolator with it switched on, you should get the same results.

    Be aware if you're using a digital tester you might get odd readings on the missing phase due to induced or capacitively coupled voltages.
    _______________________________________________

    _______________________________________________

  3. #3
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Few years ago I came acrross an old 2ph+N supply. Even the Boss man at the monkeypality was surprised. Very old supply which was never changed as the property stayed in the family all the years.

  4. #4
    Full Member
    Join Date
    Feb 2012
    Location
    Cape Town
    Posts
    41
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Hi Guys thanks for the replies...nice to know there are fellow sparkies out there who are prepared to share their knowledge and experience! It was a the problem was with the neutral not being connected to the correct neutral bar. The machine was connected to a really old Panel with some "shockingly" bad labelling but eventually found the correct bar and bobs your uncle.

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Thanks for letting us know BlueArc, it's always great to get the ending to the story and I'm happy to hear it was something relatively simple and easily fixable.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. [Question] Three phase / Single phase
    By Martinco in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 14-May-12, 10:57 PM
  2. Help please - voltage drop
    By Gei in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 21-Jan-12, 09:26 AM
  3. Touch Voltage
    By shuudeni in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Feb-11, 05:46 PM
  4. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 08-Feb-10, 09:29 PM
  5. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •