    Hi Bay Light Fittings

    I have 12 Hi bay light fittings in the factory area. All of these are fitted with 400 w MV globes.
    To convert to 105 w CFL energy savers.......................can I simply screw in the new ones, or must the ballast be bypassed ?
    A nice easy one for the fundi's !
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Usually if you're replacing with CFL you would need to make the switchgear redundant and just apply straight 220v supply directly to the lamp holder.

    I've never seen CFL's retrofitted in any other way but I would suggest you double check this with the supplier because technology is constantly changing especially in the field of lamps.
    _______________________________________________

    _______________________________________________

  3. Thanks given for this post:

    Martinco (21-Jan-13)

  4. #3
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i think the GES lampholder cfl,s are different . it comes with an electronic ballast. probably no space in the lamp due to the wattage. i have never installed them but seen it advertised. hotflo in maitland sells them.

  5. #4
    Gold Member Martinco's Avatar
    Join Date
    Oct 2008
    Location
    Rustenburg
    Posts
    927
    Thanks
    175
    Thanked 136 Times in 108 Posts
    The one's I have has an E40 base and no other switch gear was supplied. Only the lamps.
    I know that they do work if I screw them directly into a fitting with no ballast inside but I am not sure if I should try these in the new hi bay fittings fitted the other day without having the ballast removed.
    I shall have to get the sparky in again to do the change if I cannot go the easy route.
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  6. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    I have been doing it the past 3 months now every day. 400W MVs' I am replacing with either 85W or 200W CFLs'. Depending on the height, quantity of fittings in the area and required amount of light. I am also using 50W LEDs' in certain areas. Depending on the lamps you might need to change a lampholder but, if the lampholder size is the same all you need do is put your supply directly onto the lampholder. Removing the gear from the box wastes time so I just leave it there, merely bypass it. It takes long enough to get the scissor jack into place without wasting time removing redundant components.

  7. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Martinco View Post
    The one's I have has an E40 base and no other switch gear was supplied. Only the lamps.
    I know that they do work if I screw them directly into a fitting with no ballast inside but I am not sure if I should try these in the new hi bay fittings fitted the other day without having the ballast removed.
    As Sparks says, make the switchgear redundant and just connect power directly to the lampholder.
    If you know for a fact a lamp runs without a ballast connected then there's a very good chance you'll destroy the lamp quicksticks if you put it in a fitting that still has a ballast connected.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. light fittings in a fridge
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 14-Dec-12, 10:22 AM
  2. light fittings
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 29
    Last Post: 09-Aug-12, 11:04 AM
  3. thorn light fittings
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 07-Jun-12, 07:07 AM
  4. spazio light fittings
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 06-Jun-12, 07:45 PM
  5. Down lights, 220v lamps in 12 volt fittings?
    By billybob2475 in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 10-Jun-11, 10:18 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •