    What has altered recently? Any electrical additions or new appliances or even Christmas lights?

    Do you have access to a Mega tester and an RCD ramp tester? If not it's going to be difficult to find the fault(s) unless it's something obvious. The problem is that global earth leakage is a cumulative fault so you might be looking for several smaller leakage faults and it may be that none of them on their own are large enough to cause the RCD (earth leakage breaker) to trip.

    *Edit*
    0111100001110 is actually a binary message and translates as 'you'll never find me without a Mega tester'.
    _______________________________________________

    _______________________________________________

  2. #12
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Do you have any surge protection plugs?

  3. #13
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    Quote Originally Posted by AndyD View Post
    *Edit*
    0111100001110 is actually a binary message and translates as 'you'll never find me without a Mega tester'.
    hehe, good one!

    No, I have the normal hosehold multi-meters, AMP meter, ELCB polarity tester.

    Our electritian should be back from holiday tomorrow. He should be able to borrough me what I need. How does Mega and RCD ramp tester work?

    Might have surge protection scattered around. Why?
    ~Expenses will eat you alive! - My first Boss~

  4. #14
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    01111001011011110111010100100111011011000110110000 10000001101110011001010111011001100101011100100010 00000110011001101001011011100110010000100000011011 01011001010010000001110111011010010111010001101000 01101111011101010111010000100000011000010010000001 00110101100101011001110110000100100000011101000110 010101110011011101000110010101110010
    AndyD there is your binary quote!
    ~Expenses will eat you alive! - My first Boss~

  5. #15
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    ~Expenses will eat you alive! - My first Boss~

  6. #16
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    If you have had lightning or power surges recently, the caps could be faulty, you reset and there is no problem, but it will normally just trip randomly, not ever hour, but you never know, i have seen stranger thing happen.

  7. #17
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by IMHO View Post
    Earth leakage trip 7 min past the hour every hour. How do I locate the problem? This started after I replaced the old Earth leakage. Driving me mad. The problem is on one of about 7 circuit breakers or combination of them. This tends to happen only at night, but does happen here and there during day hours.
    Ok here's my 5 cents worth:
    1. You have something in your circuit that is on a timer and it comes on every hour at 7 minutes past the hour for an unspecified time. Pool motor perhaps? Jaccuzzi heater?
    2. This item does not produce enough "earth leakage" to trip the ELCB
    3. During the night you have lights that come on, and they produce enough additional "earth leakage", which when combined with the above fault cause the ELCB to trip every time the above fault occurs.
    4. During the day the lights are off but there may be additional "earth leakage" faults caused intermittently, and briefly, by other contributors such as the stove, geyser, appliances etc.

    Or your neighbour is having a lot of fun at your expense...
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #18
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    the hourly tripping is weird. maybe the house is haunted.
    but seriously i wouldnt look for the fault yet . install a 2nd earth leakage relay. split the circuits over both. then see what happens. in future it will also help with other fault finding. i have done this so many times and sometimes the fault doesnt come back. it could just be accumalative earth faults.

  9. #19
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    bergie, I will ask my electrician to do that tomorrow. A second elcb sounds like the answer, if it will split the accumulative fault. But can it be done? All the earth wires is on one common bar, is it not?

    In the meantime I have now unplugged all the laundry equipment. Still trip. Then I switched the pool pump off with its own isolator at the pump. Still trip. Now I have unplugged all fridges and freezers. Waiting for the next trip.....
    ~Expenses will eat you alive! - My first Boss~

  10. #20
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    BTW Andy, our sparkie does not want to use the meggar. He is scared he may blow up something of mine. He is advising me to play the eliminating game, till we find the culprit.
    ~Expenses will eat you alive! - My first Boss~

Page 2 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. The 4-Hour Work Week
    By derekjay in forum Book Forum
    Replies: 2
    Last Post: 16-Jul-10, 10:33 AM
  2. Charges per hour for electronics?
    By garthu in forum General Chat Forum
    Replies: 2
    Last Post: 19-Apr-09, 04:09 PM
  3. Earth hour
    By Dave A in forum General Chat Forum
    Replies: 38
    Last Post: 04-Apr-09, 11:38 AM
  4. Design a website in under an hour
    By duncan drennan in forum General Business Forum
    Replies: 0
    Last Post: 28-Aug-07, 02:49 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •