    Hi guys
    I've come across a tricky part in an installation involving compressors. According to the spec sheet I've been given they pull 105A on start up but only 44A running. So naturally I went to the SANS 1014-1 regs book to check sizing of the cable. The minimum size was 10mm (for clipped direct that is). The problem is the unit switches on and off quite often...would this affect my size of cable and if so what size would be recommended.
    Thanks

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    You would install cabling and mcb's according to the run current. The MCB's should tolerate the start current which is short in duration but still effectively protect the cabling. The volt-drop on starting would be a consideration, you don't want the voltage dropping below the operating range of the compressor even/especially on startup. The maximum cycling on/off per hour is normally specified by the compressor manufacturer, if it's cycling frequency is higher then I would suggest measures to reduce it but it wouldn't affect the cable sizing. You didn't state a cable length so I can't comment on whether 10mm is sufficient.
    _______________________________________________

    _______________________________________________

  3. #3
    Full Member
    Join Date
    Feb 2012
    Location
    Cape Town
    Posts
    41
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Thanks AndyD the cable distance is maximum 10M so it shouldn't have an affect. I do appreciate the help. I'd rather ask the question here than look like a tool ordering the wrong cable on site lol!
    What I have done though is ordered slow curve breakers to prevent start up tripping.

Similar Threads

  1. Calculating annual leave
    By KimH in forum Labour Relations and Legislation Forum
    Replies: 8
    Last Post: 07-May-13, 11:52 AM
  2. [Opinion] AC voltage / current data logger
    By murdock in forum Technology Forum
    Replies: 6
    Last Post: 18-May-11, 11:25 AM
  3. . Current Market Conditions In The Tradeshow Business
    By donaldcarter55 in forum Business Finance Forum
    Replies: 1
    Last Post: 29-Mar-10, 10:10 PM
  4. electrical over current protection
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 21-Jan-10, 03:30 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •