You'd use the measured value. The objective of establishing the actual PSCC is to ensure the protection equipment is adequately rated to handle a short-circuit situation for that particular installation, so you need to be using the actual values of the environment.
As an aside, when you have a moment read Section 8.5 of SANS 10142-1 to get where I'm coming from on what the term "calculated PSCC" means.