    Insulation resistance test

    Reading through amendment 8, i noticed that you no longer have to carry out an insulation resistance test on an exsisiting installation.

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by ians View Post
    Reading through amendment 8, i noticed that you no longer have to carry out an insulation resistance test on an exsisiting installation.
    How do you arrive at this conclusion when page 286 question 8 clearly requests the results of the insulation test.
    is there something else i am missing?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    also on page 279

    8.7.8.2 The insulation resistance, measured as follows, shall be at least
    1,0 MΩ:
    a) to measure the insulation resistance to earth, apply the test voltage
    between the earth continuity conductor and the whole system of live
    conductors, or any section of it; and
    b) to measure the insulation resistance between the conductors, apply
    the test voltage
    1) between the phase conductors, and, when relevant,
    2) between the phase conductors and the neutral conductor.
    8.7.8.3 When there are sub-distribution boards and the total insulation
    resistance is less than 1,0 MΩ, the insulation-resistance test may be
    carried out by
    a) isolating and testing the wiring between the main supply and the subdistribution
    boards, and
    b) testing, as a separate section, each sub-distribution board connected
    to all the circuits that it feeds, but the insulation resistance in each
    section shall be at least 1,0 MΩ.


    Now you see thats what i also thought until i read the new amendment no.8 carefully.

    you will find this note...

    8.7.8 Insulation resistance
    NOTE 1 Before power is connected to any new or altered circuit, the test for
    insulation resistance should be carried out to ensure there is no short-circuit or
    high impedance faults in the installation, and that it is safe to energize. Amdt 8

    NOTE 2 In the case of existing installations where the power may not be switched
    off from certain circuits in order to carry out this test, the fact that the circuits are
    subject to the supply voltage can be regarded as evident that the insulation
    resistance is compliant. Amdt

  4. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by ians View Post
    NOTE 2 In the case of existing installations where the power may not be switched
    off from certain circuits in order to carry out this test, the fact that the circuits are
    subject to the supply voltage can be regarded as evident that the insulation
    resistance is compliant. Amdt
    I suggest that only precludes installations where the power may not be switched off under any circumstances - a pretty rare occurence I should think.

  5. #5
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by ians View Post
    also on page 279

    8.7.8.2 The insulation resistance, measured as follows, shall be at least
    1,0 MΩ:
    a) to measure the insulation resistance to earth, apply the test voltage
    between the earth continuity conductor and the whole system of live
    conductors, or any section of it; and
    b) to measure the insulation resistance between the conductors, apply
    the test voltage
    1) between the phase conductors, and, when relevant,
    2) between the phase conductors and the neutral conductor.
    8.7.8.3 When there are sub-distribution boards and the total insulation
    resistance is less than 1,0 MΩ, the insulation-resistance test may be
    carried out by
    a) isolating and testing the wiring between the main supply and the subdistribution
    boards, and
    b) testing, as a separate section, each sub-distribution board connected
    to all the circuits that it feeds, but the insulation resistance in each
    section shall be at least 1,0 MΩ.


    Now you see thats what i also thought until i read the new amendment no.8 carefully.

    you will find this note...

    8.7.8 Insulation resistance
    NOTE 1 Before power is connected to any new or altered circuit, the test for
    insulation resistance should be carried out to ensure there is no short-circuit or
    high impedance faults in the installation, and that it is safe to energize. Amdt 8

    NOTE 2 In the case of existing installations where the power may not be switched
    off from certain circuits in order to carry out this test, the fact that the circuits are
    subject to the supply voltage can be regarded as evident that the insulation
    resistance is compliant. Amdt
    This is very interesting and has gone straight over my head and I am tempted to agree with Dave, only in the case where power may not be switched off
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  6. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    " the fact that the circuits are subject to the supply voltage can be regarded as evident that the insulation
    resistance is compliant."

  7. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It depends on what you are testing, if you are only doing domestic inspections, then there should be no reason why you cannot switch off. However, if you do factories and commercial inspections this could prove to be a bit tricky. I was involved with an inspection at a sugar mill, switching off the plant to do insulation resistance tests could have been tricky.

  8. #8
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    I suggest the reason why the power can't be switched off would have to be very well motivated. I certainly can't see us rolling over on this without a fight - and supporting documentation.

    Wouldn't you be nervous issuing a CoC without an insulation test?

Similar Threads

  1. [Question] Ceiling insulation R value required in Cape Town
    By smitty in forum Energy and Resource Conservation Forum
    Replies: 8
    Last Post: 04-Jul-11, 10:45 AM
  2. Eliminate all resistance
    By Dave A in forum South African Politics Forum
    Replies: 75
    Last Post: 20-Mar-11, 01:01 PM
  3. Motor winding insulation
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 18-Mar-10, 07:30 AM
  4. Ceiling insulation effect on electrical work
    By duncan drennan in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 16-Jan-10, 05:04 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •