    hi guys
    just wanna find out about doing a coc on the supply cable only.(16mm2 swa ,16 mm2 earth )
    do u still have to do the loop impedance and pssc?
    Yes, that and the voltages: supply(with and without load) and elevated.

  2. #12
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by willies View Post
    With a black computer plug the one prong is flat so to make it work he filed it so that the plug can accomodate all appliances.
    Dedicated circuits mostly do not have earth fault protection. By filing the stopper away your electrician acted illegally and exposed you and your family to electrocution. If you really must have a black plug I suggest you first replace the "compromised" socket outlet with a new one then get a "dedicated" plugtop and spray or paint it black.