Thread: 12V fitting with 220V lamps

  1. #1
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts

    12V fitting with 220V lamps

    Surely you cannot have a 220Volt GU10 Lamp in one of those silly holder things fitted into a 12volt down light. Nearly every domestic(which I try and avoid) Test and inspect for the COC I find 220Volt GU10's in 12Volt fittings and usually the connection to the supply cable isn't enclosed, just a connector block. I'm bored of dealing with customers who do the "well its worked fine like that for ages" and get annoyed when I don't sign the COC because of this. The fitting says 12V and is not earthed therefore not, to my way of thinking, compliant, Right?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think the reason that at least some of the fittings aren't earthed is that they're supposedly double insulated to Class I standards and hence don't come manufactured with any terminal to connect the earths into. I agree a standard choc-block connector with 220v cabling should be in an enclosure. Similarly transformer terminations with missing covers or shrouds would be an issue as well.
    _______________________________________________

    _______________________________________________

  3. #3
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    and does it help complaining or reporting it?

  4. #4
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Quote Originally Posted by murdock View Post
    and does it help complaining or reporting it?
    Nope - Bust my balls getting my license, don't sign unless its perfect. Don't usually sign existing work off only my own which I have done from start to finish, to much hassle sorting out other peoples F^%$ ups. They want a COC they are either going to get transformers and 12Volt lamps or get 220volt down lights put in.
    Should have used a proper electrician in the first place.

    People may learn one day its cheaper in the long run to do it right first time. If i here one more person say "well its worked fine like that for years" I'm going to zap them with my insulation resistance tester and explain that that shock just hurts and won't kill you but the one from your shitty wiring might.

    Would you sign it off Murdock??? 220volt lamp in 12 volt fitting?? And why are wholesalers selling that kind of lamp holder? Surely that can't be right? (My local Voltex doesn't sell them any more except the ones with an earth tag, like anyone will bother to connect it).

    No more domestics for me thanks.... The cowboys can keep em.

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by skatingsparks View Post
    Don't usually sign existing work off only my own which I have done from start to finish, to much hassle sorting out other peoples F^%$ ups.
    One less competitor in the market

    Quote Originally Posted by skatingsparks View Post
    They want a COC they are either going to get transformers and 12Volt lamps or get 220volt down lights put in.
    Should have used a proper electrician in the first place.
    Exactly

  6. #6
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    "Would you sign it off Murdock??? 220volt lamp in 12 volt fitting?? And why are wholesalers selling that kind of lamp holder? Surely that can't be right? (My local Voltex doesn't sell them any more except the ones with an earth tag, like anyone will bother to connect it)."

    honesty...which i suppose i shouldnt be on a public forum...a couple of years ago i would have been were you are right now complaining about...but lately i have a new policy...if you cant beat and the powers that be dont want to improve the industry...join them...i can also do a coc in 15 minutes..and looking for the kind of issues you are finding...it hard to find because most times i dont climb in the roof anymore...i just look from the trap door with a torch and if it looks ok...to fill out the coc takes another 10 minute...that pretty much all you gona get for R950 i charge for a domestic installation...i have also standardised my coc to save money...all the info on all my cocs are exactly the same if they pass...i just fill in the address details...i pay my labourer to fill them in by the dozen...it saves me hours...until there is some improvement in the industry and there is some sort of policing introduced...why waste your time getting all worked up...i use to get all worked up and report stuff and waste time...now i go with the flow...put my blinkers on...and actually challenge any other electrical contractor...AIA...or dol memeber to take me to task with regards to a coc...i have filled out...come on i dare you....i have a list so long by the time the court gets back to me i would have retired.

  7. #7
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    murdock that post was so depressing i had to take a pill. i dont stress when i climb in a roof and see a big mess. i see dollar signs.
    i try to do my work properly regardless of what others do.
    regarding the 12 volt downlighter fittings with 230 volt lamps. its been discussed at length and i still dont know if its acceptable or not.
    i dont install it like that,but if i find it with proper terminations,etc then i pass it. the 12 volt frame can be classed as double insulated.

  8. Thanks given for this post:

    Dave A (11-May-12)

  9. #8
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Hopefully murdock's post 6 was mostly sarcasm

  10. #9
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by Dave A View Post
    Hopefully murdock's post 6 was mostly sarcasm
    We are so accustomed to it that we forget Murdock's closing line: "Disclaimer: Hmmmmm. I know you think you understand what you thought I said, but I'm
    not sure that what you heard is what I actually meant!"

    As for double insulated 12V downlight frames, where on earth does that idea come from? If a 12V set is bought that comes with double insulated transformers, yes, the set would be double insulated because of the transformer insulation. Replace/remove the double insulated transformer and you lose the classification.

    Or can someone please explain to me where the "double insulation" is when you have a metal ring with a spring on it?

  11. #10
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    dave please dont pull my sponsorship....

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Installation of 220V downlights
    By Oblivious in forum Electrical Contracting Industry Forum
    Replies: 105
    Last Post: 14-Feb-20, 09:57 AM
  2. Down lights, 220v lamps in 12 volt fittings?
    By billybob2475 in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 10-Jun-11, 10:18 AM
  3. A Erwin on compact fluorescent lamps rollout programme
    By I Robot in forum Electrical Load Shedding Forum
    Replies: 4
    Last Post: 05-Sep-08, 06:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •