Results 1 to 7 of 7

Thread: Loop Impedance

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    New Member
    Join Date
    Apr 2012
    Location
    Edenvale JHB
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Loop Impedance

    So glad to find a place where I can ask questions.

    Is there a chart or table that can help me determine the acceptable loop impedance and PSU results on an existing installation.

  2. #2
    Email problem
    Join Date
    Apr 2012
    Location
    Sandton
    Posts
    9
    Thanks
    0
    Thanked 1 Time in 1 Post
    From SANS 10142-7 : 8.7.5, At the main switch, the impedance shall be such that an earth fault current double the rated current (or higher) of the main protective device automatically disconnects the supply to the installation. The formula
    for a 60 amp supply : voltage over 2 x current ( V/2I ) ie 230 divided by 120 = 1.92ohms. A reading less than 1.92ohms is acceptable. (p.s. post again if you need this test described in laymans terms)
    Your second question - I presume you mean PSC (prospective short circuit)(rating). What is the rating of your breakers?
    Probably 5kA or 5000amps (marked on the breaker) - your reading must be less than that.

  3. Thanks given for this post:

    Dave A (27-Apr-12)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Welcome to the forum Mojakoki
    _______________________________________________

    _______________________________________________

  5. #4
    New Member
    Join Date
    Apr 2012
    Location
    Edenvale JHB
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks! I was recently told by the council we can't accept readings above 1.4ohms. Got a bit confused.

    On 3 phase - would I then use 380V or 230V.

  6. #5
    Email problem
    Join Date
    Apr 2012
    Location
    Sandton
    Posts
    9
    Thanks
    0
    Thanked 1 Time in 1 Post
    If your reading is high, (too high for your Council's liking), consider installing an earth rod.
    Pretty sure you would use 230V for a 3 phase installation as you are testing the earth resistance back to the transformer where the suppliers earth is supplied.

  7. #6
    Suspended
    Join Date
    Oct 2020
    Location
    https://t.me/pump_upp
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi Guy's,

    Anybody that can assist with a excel sheet for the calculation of Loop impedance and Ipscc. I have a warehouse where between council and client i have 240mm x 4c cable about 10m. From there i have 3 x 150mm 4c cables to main mcc about 70m. Need to calculate. I have all the transformer information.

    Thanks in advance.

    Conrad

  8. #7
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by CGelectrical View Post
    Hi Guy's,

    Anybody that can assist with a excel sheet for the calculation of Loop impedance and Ipscc. I have a warehouse where between council and client i have 240mm x 4c cable about 10m. From there i have 3 x 150mm 4c cables to main mcc about 70m. Need to calculate. I have all the transformer information.

    Thanks in advance.

    Conrad
    Hi

    I have a Schneider slide rule on spreadsheet with explanations on how to read it as well as other interesting tabs for transformer currents etc. Its over 2MB so I cant attach it here. If you can send me mail I will send it to you. I have a second spreadsheet that I have compiled that I can send. The formulas have not been confirmed by an engineer but so far the answers have been correct.

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •