Thread: Disconnecting a gate motor

  1. #1
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts

    Disconnecting a gate motor

    Elsewhere in this forum I made a statement that even though a gate motor is fed from a removable plug-top in the garage it should still be controlled from a disconnection device within 1.5 meters from it. After researching the regulations for answers to another question I have come across some information which I believe proves me wrong.

    6.9.3 Disconnecting devices for equipment Amdt 3
    6.9.3.1 An appliance or equipment that is not supplied from a
    socket-outlet, including equipment automatically or remote controlled,
    shall be capable of being disconnected from the supply by an easily
    accessible switch-disconnector. The disconnector shall be mounted (if
    not specified elsewhere in this part of SANS 10142 (SABS 0142), but
    excluding luminaire circuits) (see also 6.16.1.4) Amdt 1
    a) within arm's reach from the terminals of the appliance, or
    b) in a distribution board, if the device is capable of being locked in the
    open position.

    NOTE 3 The removal of a plug from a socket-outlet is a means of safe disconnection.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  2. #2
    Suspended
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    893
    Thanks
    8
    Thanked 61 Times in 54 Posts
    Yep within arms distance from the device.

  3. #3
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    and this just proves how would be common sense...not to use a socket outlet in the garage because unless you cut the plug off while working on the circuit..anyone could plug it back in.

    how many electrician carry a locking devise for circuit breakers?

  4. #4
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts

    Smile

    Quote Originally Posted by murdock View Post
    and this just proves how would be common sense...not to use a socket outlet in the garage because unless you cut the plug off while working on the circuit..anyone could plug it back in.

    how many electrician carry a locking devise for circuit breakers?
    Whilst I do agree with what you are saying my emphasis is on interpreting the regulations as they stand and not trying to change them. I work with these regs every day of my life and I would like to understand them completely 100%

    You see I do not install these devices at all but they do come into my sights when issuing a COC.
    The information I am getting from this part of SANS is that you may use the plug in the garage as disconnecting device.
    The cable to the motor cannot be anything other than Norsk, flat twin and earth or GP wire in a conjute piping, whether it plugs in or not and Cabtyre and "Speaker cable" (ripcord) are out.
    The requirement for an isolator at the gate for a circuit that is fed from a plugtop does not exist.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  5. #5
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    the key word is "lockable" if not within arms reach . a socket outlet wouldnt be lockable.

  6. #6
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    Quote Originally Posted by murdock View Post
    and this just proves how would be common sense...not to use a socket outlet in the garage because unless you cut the plug off while working on the circuit..anyone could plug it back in.

    how many electrician carry a locking devise for circuit breakers?
    or should i say how many "electricians" know what a circuit breaker lockout looks like.

  7. #7
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by bergie View Post
    the key word is "lockable" if not within arms reach . a socket outlet wouldnt be lockable.
    Bergie I agree with both you and Murdoc on this, it just doesnt make me feel safe pulling a plug I cannot see.
    As far as I can see the regs do not require you to do anything other than that though.
    Does anyone else know of any passage I may have missed?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by murdock View Post
    how many electrician carry a locking devise for circuit breakers?
    I have a kit with several different MCB and MCCB lockout devices aswell as colour coded padlocks and signage, there's one on each of our vehicles as well. They don't cost a fortune and they're an HSE requirement on many sites nowadays.

    There are lockout covers you can fit on plugs and padlock to prevent them being plugged in again so a plug can be considered a lockable disconnect if the right device is used.
    _______________________________________________

    _______________________________________________

  9. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by Leecatt View Post
    Bergie I agree with both you and Murdoc on this, it just doesnt make me feel safe pulling a plug I cannot see.
    As far as I can see the regs do not require you to do anything other than that though.
    Does anyone else know of any passage I may have missed?
    6.16.5.1.5 b) visible from the motor, or

    If you're relying on a plugtop disconnector in the garage, options a, c and d probably won't apply in most instances.

    Sidenote: The "housed in a lockable enclosure other than a distribution board" does provide an interesting option to bring existing installations up to code.

  10. Thanks given for this post:

    ACEsterhuizen (02-Mar-16)

  11. #10
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    Quote Originally Posted by AndyD View Post
    There are lockout covers you can fit on plugs and padlock to prevent them being plugged in again so a plug can be considered a lockable disconnect if the right device is used.
    please post a pic or a link...this is something i dont have or have i ever seen...you learn something new everyday.

Page 1 of 7 123 ... LastLast

Similar Threads

  1. VAT on motor oil
    By J7J in forum Tax Forum
    Replies: 2
    Last Post: 12-Jan-12, 09:46 PM
  2. Electric Motor or Generator ?
    By daveob in forum Electrical Load Shedding Forum
    Replies: 10
    Last Post: 17-Oct-11, 06:01 PM
  3. disconnecting and reconnecting electricty
    By murdock in forum General Business Forum
    Replies: 18
    Last Post: 04-Mar-11, 03:55 PM
  4. Motor winding insulation
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4