    Help please - voltage drop

    Good day
    I wired a db for a friend, we used 4mm2 twin and earth for 70m distance protected by a 35amp cb. I allready know the cable is to small for the voltage drop over the distance.But with no load i measure 212volts and 11 volts on the neutral. The elevated voltage on the neutral is what is bothering me. and also as soon as i put the plugs or aircon breaker on the voltage drops to less than a 100volt but there is no load so there should not be a vd????
    Any help would be appreciated.
    Johan

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Can you clarify a few things please?

    You say you 'wired a DB' using 4mm cable, is this actually a subDB running supplied from his main DB?
    Did you export the earth or have you installed a spike at the remote location?
    The 11 volts you have on the neutral, were you using a digital or analogue voltmeter and was this with reference to earth?

    as soon as i put the plugs or aircon breaker on the voltage drops to less than a 100volt but there is no load so there should not be a vd????
    I don't understand this part at all I'm afraid, please explain.

    Can you say what load you will have on his cable ie air-con's, lighting, hot water heaters, etc?
    _______________________________________________

    _______________________________________________

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    I think that you may be measuring what I call capacitive induced voltage in the long cable. Basically a capacitor is two conductors, with a dielectric between them, so air is a a dielectric, and so is PVC plastic which usually covers the conductors. The closer and longer the length of the conductors, the higher the capacitance value, and because it is AC, it is transferred through the PVC. That is that there is power on this very long cable although not being consumed, is still there, and you are measuring the conductors against the earth. Now when you plug your equipment in, especially electronic devices, there are surge protection devices inside the equipment, along with capacitors between earth, live and neutral, which acts as suppressors and absorb electrical spikes that may be induced in the supply due to inductive loads being switched. So now the internal suppression components act as impedance's albeit high, still act against the cable and reduce the voltage as you have experienced. The moment you connect a load to the cable, you will get the readings you are expecting.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    what is the voltage at the main d.b. it should not drop 18 volts at the end of the cable with no load. i reckon the cable could be damaged,probably the neutral wire. check the n-e voltage at the main db. and compare to the end of the cable.

Similar Threads

  1. Touch Voltage
    By shuudeni in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Feb-11, 05:46 PM
  2. Mains voltage logger
    By duncan drennan in forum Technology Forum
    Replies: 16
    Last Post: 05-Feb-11, 03:33 PM
  3. Vodacom signal drop
    By twinscythe12332 in forum Technology Forum
    Replies: 3
    Last Post: 11-Oct-10, 06:31 AM
  4. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 08-Feb-10, 09:29 PM
  5. Drop your price.
    By Dave A in forum Entrepreneurship and Business Management Forum
    Replies: 9
    Last Post: 10-Oct-09, 08:51 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •