    Lead cable

    Howzit guys

    Please if i can get some info,im busy re-routing an old lead cable for a client,gonna install it in a new board,what would be the easiest way to get an earth off of that cable as there is no earth "they used the lead as earthing in the old days",and i cant run an external earth as it is to far to dig....tx in advance

    Colin

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Lead cabling is very difficult to work with. The bending radius's used to be very long, it's very difficult to gland and joint and I'm not sure you can use brass and copper fittings due to it being a dissimilar metal. In the good old days the lead cable would have had a gland or collar sweated on (similar to soldering on a large scale) unless it was an air pressurized cable in which case the termination procedure was far more complicated.

    The electrical regs don't specifically cover lead cabling as far as I know but I would say a separate CPC would be necessary for compliance. I would look at installing a local earth spike if trenching is an issue. I would also test the insulation of the cable before you even quote on this job, the paper or cotton insulation that was often used on the conductors is notoriously hygroscopic and old cables often didn't maintain a good insulation value.

    My gut feeling would be to install a new cable entirely to avoid future problems but it's your call.
    _______________________________________________

    _______________________________________________

  3. #3
    Email problem
    Join Date
    Jul 2011
    Location
    Boksburg
    Posts
    24
    Thanks
    0
    Thanked 1 Time in 1 Post
    Ok yeah great tx for the info,I was also thinking to install earth spike buried at least 2m down with coarse salt to get proper earthing....

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    i use a cable joiner when i have join or gland off those old cables. theres an ex city council joiner in cape town i normally use. they should have all the special tools etc.
    incidentally a 2,4 m earth spike here is normally too short. i always install 2x 2,4m on top of each other. spreading short spikes out doesnt seem to work.i need to get to the water table in this sandy ground.

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by bergie View Post
    incidentally a 2,4 m earth spike here is normally too short. i always install 2x 2,4m on top of each other. spreading short spikes out doesnt seem to work.i need to get to the water table in this sandy ground.
    I just installed an earth spike in the southern suburbs of Cape Town and we needed 7 x 2.3 meter spikes on top of each other to get a decent reading.
    _______________________________________________

    _______________________________________________

  6. #6
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    thats deep.the customer can share the cost with somebody in china.
    i found out how the suburb of ysterplaat got its name.theres a impenetrable plaat of yster about a metre deep. not nice for earth spikes.

  7. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I tested with each spike that went in and was sitting with >1000Ω after the first two spikes
    _______________________________________________

    _______________________________________________

  8. #8
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    What about a earth mat

  9. #9
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    what about the suppliers earth?

    in durban the supply earth is considered adiquate

  10. #10
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    A clamp around the cable would work, as AndyD points out, the bottom line is: Earth Continuity Reading.

Similar Threads

  1. cable sizes
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 20-Mar-11, 08:50 PM
  2. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •