Connecting batteries in parrallel.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #1

    Connecting batteries in parrallel.

    I'm struggling to understand why, when connecting parrallel batteries, the positive to the inverter is taken from battery 1 and the negative from battery 2 or 3, depending on how many are in parralel.

    Can someone explain, technically, why this is so and what will happen if both the positive and negative are connected to the same battery ?q
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    When you take both leads from one battery the current/power tends to come from the first battery and then it looks at the rest , so you tend to use more on battery 1 and end up with imbalance - same when charging , just in reverse

    When you take the lead from first and last then you tend to force all the batteries to work the same and stay balanced

    They talk about keeping the individual cells at not more then 300mv difference when charging and discharging and should be 0mv difference at standby , with 100mv difference being to high.

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #3
      Another point to note that I follow, I keep all the battery wires the same length. This ensures that the current is balanced to all batteries.
      I also use a battery disconnect switch on each battery. Makes maintenance easier.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • Derlyn
        Platinum Member

        • Mar 2019
        • 1748

        #4
        Thank you, gentlemen. Much appreciated 👍 Got some changes to go and attend to on an installation 😉

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #5
          I connect the batteries in parallel cascade, so that I only need one DC battery disconnect.

          I am busy with a 3 phase inverter, with 3 batteries on a rack so that the jumpers are short we just install one disconnected on the side of the rack.

          As mentioned all the jumpers are the same length and from the 2 ends to the disconnect the batteries are the same length.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.