    #16
    Someone I know had Deye installed but says he is going to change the logger to a Synsynk because the Deye has to be controlled by the installer.

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #17
      The Sunsynk installer has full control over the Sunsynk unit. if the customer doesn't pay the bill I can shut the system down. My customers dont have this problem because all their systems are paid up in full.

      The old dongle used Solarman software.

      At one stage you could buy a sunsynk dongle and fit it to a deye unit which is built in the same factory, they look and use the same components, only the software is different (so I am told) and of course the price.

      People got smart and started buying and fitting the Sunsynk dongle to the Deye units for way cheaper than buying a Sunsynk unit with a a free dongle, how true this is I couldnt tell you because I have never done it.
      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

      Comment

      • Isetech
        Platinum Member

        • Mar 2022
        • 2274

        #18
        What is going to be interesting, something I need to check on the other units we have installed. I am going to change the frequency from 50 to 60 and see if the limits reset automatically.

        Another lesson learnt with these Sunsynk units, never assume anything, rather press ok, then go back and check the setting has activated, then run through all the other settings and make sure they have adjusted accordingly.
        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

        Comment

        • Isetech
          Platinum Member

          • Mar 2022
          • 2274

          #19
          Something else you need to check is the software is the latest version and do a firmware update, if required.
          Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

          Comment

          • Isetech
            Platinum Member

            • Mar 2022
            • 2274

            #20
            By the way I am new to Sunsynk products, yes I am going to ask the dumbest of questions and yes 99 % of the issues are going to be installer related, hence the reason I need good technical support, at the press of a button, from people who have experience with these units, who can assist and advise me when I get stuck with silly challenges or installer errors.

            It is a good product and one of the reasons I have chosen to install these units on the majority of my customers sites. The people at Sunsynk are improving the product by the day. We will continue to install products like Victron (the Rolls Royce of inverters), axperts and Luxpower for the customers who dont have the budget for the more expensive units.

            Something I have learnt recently, no matter where you buy the unit, the technical support is international (+27 10 100 3589). If you buy the unit from ARB or Voltex the technical support is the same. You call the number, it takes you to a call centre in the UK, you tell them the problem them they will redirect you to someone somewhere in the world, make sure your telephone line has lots of spare minutes.
            Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

            Comment

            • Isetech
              Platinum Member

              • Mar 2022
              • 2274

              #21
              Yes anyone can buy a Sunsynk inverter or battery, DIYer, green card holder or registered electrician. We all know that no matter how much everyone is trying to take control of this industry, nothing is going to change for a while yet.

              Because technical support is international, it makes no difference where you buy the unit, price becomes the main factor.

              If you buy the unit from Voltex (bit slow with their response to quote requests) or ARB (fast response and good prices), you will still use the same technical support. Just make sure they have stock before you do the bank transfer, this is a tricky situation.

              It seems the stages of load shedding determine the stock and pricing, some will tell you it is the exchange rate
              Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

              Comment

              • Empowered
                New Member
                • Apr 2023
                • 2

                #22
                Hi Isetech, hello and thanks for this informative thread.

                This caught my attention and I'm wondering if you could explain more please...

                Originally posted by Isetech


                As I mentioned earlier, a 550 watt panels with a max current 13 amps cannot be used with a 5kva Sunsynk inverter (11 amp), so you would have to get an 8 kva inverter or get smaller panels.
                Someone mentioned this to me recently too. Why can't one use 550watt panels with a 5kva inverter?

                Comment

                • Isetech
                  Platinum Member

                  • Mar 2022
                  • 2274

                  #23
                  With the limited knowledge I have of solar design, I stick to the data sheets.

                  I have read of others using 550 watt panels.

                  When I do the install at my workshop, I might try it to see what happens.

                  Do you have any input to share ?

                  Living and leanring by the day, always open to suggestions or a bit of technical advice.







                  Originally posted by Empowered
                  Hi Isetech, hello and thanks for this informative thread.I havent

                  This caught my attention and I'm wondering if you could explain more please...



                  Someone mentioned this to me recently too. Why can't one use 550watt panels with a 5kva inverter?
                  Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                  Comment

                  • Justloadit
                    Diamond Member

                    • Nov 2010
                    • 3518

                    #24
                    Its not the panel wattage size, it has o do with the current the panel can provide.
                    Only until recently, PV panels would produce a voltage and the current never exceeded 11Amps, these panels are now providing up to 16Amps.

                    The electronics in the inverter are rated at 11Amps, so the 16Amps exceeds the inverter rating.
                    When the inverter goes into a MPPT mode, it loads the panel until it reaches the knee of the panel wattage, in the rated case the string would not exceed 11A, however with the higher current panels, the inverter will receive 16A, in a short while this will destroy the boost electronics due to over current.
                    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                    Comment

                    • GCE
                      Platinum Member

                      • Jun 2017
                      • 1473

                      #25
                      Originally posted by Empowered
                      Hi Isetech, hello and thanks for this informative thread.

                      This caught my attention and I'm wondering if you could explain more please...



                      Someone mentioned this to me recently too. Why can't one use 550watt panels with a 5kva inverter?
                      Ratings on electrical equipment are there for a reason - The design of the electronics , heat dissipation etc. on the MPPT
                      Would be like taking an 11Amp contactor and running 13 Amps through it every day for an hour or two - It is going to fail prematurely which means your expected 5 year warranty will fall away as all that information is logged
                      The voltage on the MPPT is even more critical as edge of cloud effect can lift that voltage by 20% depending on time of day.

                      You would not buy a 1/2 ton bakkie to take a 750Kg load at red line on the motor between PE and Cape town as a courier service and expect the bakkie to give you the same life expectancy - Brakes will fail prematurely , motor will go through head gaskets , overheat on hills etc - You would expect problems , same thing with an MPPT that is been driven hard.

                      Comment

                      • Isetech
                        Platinum Member

                        • Mar 2022
                        • 2274

                        #26
                        Besides all the technical reasons, product warranty is the most important factor.

                        Even when installing the units, I stick to the suggested spacing etc.
                        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                        Comment

                        • Justloadit
                          Diamond Member

                          • Nov 2010
                          • 3518

                          #27
                          Originally posted by GCE
                          Ratings on electrical equipment are there for a reason - The design of the electronics , heat dissipation etc. on the MPPT
                          Would be like taking an 11Amp contactor and running 13 Amps through it every day for an hour or two - It is going to fail prematurely which means your expected 5 year warranty will fall away as all that information is logged
                          The voltage on the MPPT is even more critical as edge of cloud effect can lift that voltage by 20% depending on time of day.
                          Since a PV panel is a current source, the only change in the voltage of the panel is due to the effect of temperature.
                          The open circuit voltage between say -5°C and 25° to 55°C can say as much as 5V up when cold to down when hot from the specification sheet which is done at 25°C
                          What changes is the amount of current the panel provides. It can vary fr0m 0.5A early in the morning say at 08H00 to FSD amps example 11A between 11H00 to 13H00during a sunny day. Provided the Azimut angle is correct and panels facing North in the southern hemmisphere, and that there are no shadows and the panel is clean and free from bird droppings. As clouds come over, the MPPT voltage remains the same, only the current changes.
                          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                          Comment

                          • Empowered
                            New Member
                            • Apr 2023
                            • 2

                            #28
                            Hi Isetech, GCE and Justloadi - thanks for your insights - very helpful and gives me a proper understanding of the issue.

                            I'm a novice at solar - I've been getting quotes for a 5KW PV system and I've come across so many different perspectives from the various installers, this issue being one of them. Some have given quotes for 450 panels, others 550 and one told me you can't use the 550 on a 5kw, while another said it makes no difference.

                            I googled to find out and found this thread. It's great to have confirmation and understanding - thanks! It makes sense that more hardcore current would put strain on an inverter.

                            Makes me wonder if this is part of the reason there's such a wait for Sunsynk inverter returns and repairs. I've seen people mention this on Facebook - maybe it's because they need to assess why the inverters that are brought in have problems and this sort of thing could be something they look for if all that information is logged.

                            Comment

                            • Isetech
                              Platinum Member

                              • Mar 2022
                              • 2274

                              #29
                              I dont think it is the solar panels are causing all the problems, I have heard that it is more to do with overloaded relays.

                              People have this idea that you can connect a 5 kva and not split the essential and non essential, just load eveything onto the inverter.

                              There are ways to do it, however you would need to install devices to control the load, like a PLC or smart swtiches or an ECU.

                              Undersized cables, another issue, some people use 2.5 mm as the grid supply and the UPS for a 5 KVA inverter, then they slap a roof full of panels and suddenly you have pass through current going up to 30 amps. This also puts huge strain on the inverter.

                              This is why it is so important to have detailed documents about the sytem and why it is important to lock the settings and not let people make adjustments onece commsioned.




                              Originally posted by Empowered

                              Makes me wonder if this is part of the reason there's such a wait for Sunsynk inverter returns and repairs. I've seen people mention this on Facebook - maybe it's because they need to assess why the inverters that are brought in have problems and this sort of thing could be something they look for if all that information is logged.
                              Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

                              Comment

                              • Isetech
                                Platinum Member

                                • Mar 2022
                                • 2274

                                #30
                                If you are looking for solar panels for a 5 kva Sunsynk inverter, I would say the 460 watt JA panel would be the most suitable if you have the space on the roof.

                                If you dont have a large roof space, then scaling down and using smaller panels might be a better option because then you can double them up and maximize the avaialbe roof space.

                                I see some people mount the panels right to the end of the roof top bottom and sides, I hear it is not a smart idea, something to do with lightning and when it rains the wate rover shoots the gutter.