Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
This is an old thread, im shocked to see a Mecer ups integrated into a DB. i see no earth spike wiring, i could just assume that neutrals in this install are common across the utility and inverter.
an earth neutral bond is essential for circuits connected to the inverter in conjunction with a RCD on the inverter output after the bond.
the changeover switch effectively disconnects the earth bond on the utility side, hence a separate bond is not only allowed but a requirement to be compliant with SANS10142
i hope this has been corrected since this photo was posted as you have effectively removed the protective shell around everything connected to the inverter
I am shocked to see 99 percent of pictures being posted on social media.
Please attach the code or which SANS and the page.
Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.