    Electric Heating Load Rating

    Hi all a unusual query landed in my inbox this morning a electric heating system is rated 6kw now it is supplied via a 3 phase supply is it 6kw per phase or as in a 3 phase motor is it total load 6 kw in other words is it 2kw per phase or6 kw per phase I asked them to check the amperage rating but agai is it collective amps or amps per phase lets have some answers
    thanks
    Mike
  • duncan drennan
    Email problem

    • Jun 2006
    • 2642

    #2
    Typically motor ratings would be for the entire motor, i.e. 6kW total power consumed (not 6kW per phase).

    |

    Comment

    • Dave A
      Site Caretaker

      • May 2006
      • 22810

      #3
      The power rating should be for the unit on which the power rating is being given.

      As an aside: this raised an interesting discussion at the office on the consequences of a phase going down i.r.o. motors vs heaters.