AC control DB for inverters

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Tradie
    Silver Member

    • Feb 2025
    • 329

    #1

    AC control DB for inverters

    Do we need an AC control box.

    I see something that has become common practise, instead of fitting an AC control DB, a 4 pole isolator is used with a 4 core cable.

    1 x 4 core cable from the main DB, spilt in the main DB for the inverter supply and the other to the essential part of the DB.

    1 x 4 pole isolator at the inverter and 1 4 core cable from the isolator to the inverter.
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    Originally posted by Tradie
    Do we need an AC control box.

    I see something that has become common practise, instead of fitting an AC control DB, a 4 pole isolator is used with a 4 core cable.

    1 x 4 core cable from the main DB, spilt in the main DB for the inverter supply and the other to the essential part of the DB.

    1 x 4 pole isolator at the inverter and 1 4 core cable from the isolator to the inverter.
    That is illegal - common logic will without putting regs into place - If I switch the isolator off i am not isolating all supplies as on the DB side the supply from inverter will be live

    The cable will not be isolated and still have 2 cores live

    Screams danger from all directions