    Is this outside fuse box legal?

    Dear members,
    An electrical contractor installed a fuse box on an outside wall. It’s under a roof overhang. I asked if this outside fuse box should be in a box, protected from the elements. He said no it’s legal the way it is. Can experts tell me if this is compliant?
  • Dave A
    Site Caretaker

    • May 2006
    • 22810

    #2
    Please post a photo of the fuse box and location. It will make it easier to give informed comment.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #3
      5.6 Environmental conditions.

      5.6.1. Electrical equipment shall be able to withstand the environmental coditions of the location in which it is installed. However, electrical equipment may be protected to allow it's use in a particular environment for which it is not designed, provided that the environment shall allow for the normal heating and cooling of the equipment.

      Above is the appropriate standard.

      What this means, as far as a DB or as you call it a fuse box is concerned, is that the contents of the DB ( circuit breakers etc ) need not be weatherproof but the enclosure (DB) should be.

      I work on the assumption that if it's outside, irrespective of it being under an overhang, it is effected by the weather, therefore I use a weatherproof enclosure.

      It doesn't make any sense not to. The price difference between a "normal" and weatherproof DB is so little, I regard it as negligable.

      Comment

      • Gerhard003
        New Member
        • Dec 2024
        • 4

        #4
        Click image for larger version

Name:	IMG_1076.jpg
Views:	1
Size:	79.1 KB
ID:	266360 location of box

        Comment

        • Gerhard003
          New Member
          • Dec 2024
          • 4

          #5
          Click image for larger version

Name:	IMG_1077 2 copy.jpg
Views:	1
Size:	70.2 KB
ID:	266361

          Comment

          • Gerhard003
            New Member
            • Dec 2024
            • 4

            #6
            now that would help!
            Photos added below

            Comment

            • Derlyn
              Platinum Member

              • Mar 2019
              • 1748

              #7
              I don't think one can refer to it as illegal, however, in my opinion, it's not ideal.

              I would have used a weatherproof DB.

              Lets hear the opinions of the other toppies.

              Comment

              • skatingsparks
                Silver Member

                • Mar 2008
                • 375

                #8
                It's a case of "don't like it but couldn't fail it". Yes, I would have used IP rated but it looks like it's not going to be exposed to the elements
                Can't see for sure but looks like that's not a double pole main switch on the far left - that would be a problem for me.

                Comment

                • Thys LOW Elektries
                  Silver Member

                  • Jan 2021
                  • 269

                  #9
                  It looks like the tray of the DB is a flush tray, is it advisable to use a flush tray on the surface?

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4946

                    #10
                    I'm not sure about those drip loops in the cables being that close to the DB....
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • Thys LOW Elektries
                      Silver Member

                      • Jan 2021
                      • 269

                      #11
                      I still say "A Su1 box with trunking would have looked a lot more professional" but being able to cut an R250 or R300 of your R?? 000 quote to get the job is most important!?