Inverter sizing mystery

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #1

    Inverter sizing mystery

    I have hit a block on figuring out what I see as a problem.

    We did a logging on a set of escalators to install back up power to last for the 2 ,5 hrs. of load shedding
    We logged 3 phases being even at +/-38amps with a PF of +/-0.7 and it was pretty constant as can be expected. Initially on installing the logger we double checked with a tong tester and the readings matched.
    Did the calculation and got +/-26Kva which is around 18.5Kw which again matched logger data - So we double check , voltage is 400v , no current on the neutral - voltage between neutral and earth is perfect as transformer is 20m away.
    There are spikes of 70 amps as the system is star delta ( there are reasons that VSD are not installed, which would be an obvious cost saving )

    My mind tells me that I need to size according to actual amps drawn and KVA so I estimate an inverter at 50KW to cover any spikes and allow a decent charge time in between load shed cycles , and a battery bank of 70Kwh
    I check with suppliers and they are nervous as my logger has recorded at 1sec intervals , they request we install a 1msec interval as they have bumped heads previously where the spikes are higher and longer then initially thought but agree that maybe the above system will be OK
    I sit with the client and run through the numbers where after they almost fell of the chair as we looking at around 800K for the system.

    They show me another price that is using 2 x 12Kw inverters in parallel with 40Kwh of batteries

    My reaction was that it will not work and if it does it will not last the 2,5Hrs of load shedding

    The 2 x 12Kw system gets installed - After install I am told everything works perfectly
    I have limited access to the system and check the inverter readings - On grid it shows current drawn at 25amps on one inverter and 14 Amps on the other which adds to my original +/-38Amps - I would be concerned on the imbalance but more concerning was that the inverter showed and accumulated 6 Kw load which makes no sense

    We run a grid failure test - The output of the 2 inverters shows current draw at +/- 32 Amps 380v with a multi meter , no current on neutral and the inverter shows an accumulate 6 kw load - The batteries deliver 6Kw of energy and after 2 hours show a decrease of 40% which matches the +/- 6Kw of load draw which equates to +/-16Kwh of battery

    What makes no sense to me is how the load still appears to be +/- 21Kva 14Kw and the actual draw from batteries and inverter show +/-6Kw
    Used 2 different makes of multi meters
    The slight discrepancy in multi meter readings and calc being offgrid 21Kva to 26Kva I would put to voltage and PF but to try explain the 6kw inverter draw is my struggle

    Can anybody think of a plausible reason ?
  • Dave A
    Site Caretaker

    • May 2006
    • 22810

    #2
    I understand that the communication between inverters to have them running a load in parallel is to synchronise the phases... and not much else.

    So is the 6kw draw just for that inverter? i.e You need to sum the value of each inverter to arrive at the total load.
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • GCE
      Platinum Member

      • Jun 2017
      • 1473

      #3
      Originally posted by Dave A
      I understand that the communication between inverters to have them running a load in parallel is to synchronise the phases... and not much else.

      So is the 6kw draw just for that inverter? i.e You need to sum the value of each inverter to arrive at the total load.
      each inverter is showing 3 KW - the figures above I have accumulated already

      Off grid , on battery supply power , each inverter shows 16amp output on load with multi meter but only draws 3 Kw from battery and when I measure the current draw on each battery with a multi meter it shows 60 amps DC at 50 v = 3Kw

      Comment

      • Dave A
        Site Caretaker

        • May 2006
        • 22810

        #4
        The capacitors in the inverters are doing some serious power factor correcting?
        Last edited by Dave A; 10-Jul-24, 09:38 AM. Reason: correction - inverter plural
        Participation is voluntary.

        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

        Comment

        • GCE
          Platinum Member

          • Jun 2017
          • 1473

          #5
          Have attached screen off inverter showing readings along with DC tong test and AC tong test on load

          Click image for larger version

Name:	20240708_090054.jpg
Views:	1
Size:	38.1 KB
ID:	266337
          Click image for larger version

Name:	20240708_090103.jpg
Views:	1
Size:	36.1 KB
ID:	266338
          Click image for larger version

Name:	20240708_091445.jpg
Views:	1
Size:	20.5 KB
ID:	266339
          Click image for larger version

Name:	20240708_091509.jpg
Views:	1
Size:	19.6 KB
ID:	266340
          Click image for larger version

Name:	20240708_091828.jpg
Views:	1
Size:	37.1 KB
ID:	266341
          Click image for larger version

Name:	20240708_092049.jpg
Views:	1
Size:	30.9 KB
ID:	266342

          Comment

          • GCE
            Platinum Member

            • Jun 2017
            • 1473

            #6
            Originally posted by Dave A
            The capacitors in the inverters are doing some serious power factor correcting?
            If that was the case I would expect PF to be reading 1 and the calc would then be P = 400*1.73*1*16 = 11Kw per inverter and I would be back to +/- 22kw total load

            Comment

            • Derlyn
              Platinum Member

              • Mar 2019
              • 1748

              #7
              Are the batteries common to both inverters or has each inverter got it's own set of batteries?

              Comment

              • GCE
                Platinum Member

                • Jun 2017
                • 1473

                #8
                Originally posted by Derlyn
                Are the batteries common to both inverters or has each inverter got it's own set of batteries?
                Think they could each have there own - separate fuses etc to each inverter - I took readings off battery cable going into the inverter

                Comment

                • Dave A
                  Site Caretaker

                  • May 2006
                  • 22810

                  #9
                  Originally posted by GCE
                  If that was the case I would expect PF to be reading 1 and the calc would then be P = 400*1.73*1*16 = 11Kw per inverter and I would be back to +/- 22kw total load
                  Your 16 amp reading seems to be a sum of the current on all three phases.
                  You multiply by 1.73 when you are using the current for one of the 3 phases ... (and this assumes a balanced load).

                  Edit: Rather use the average current per phase for the calculation.
                  And perhaps 380 rather than 400 as they are running at 220V per phase.
                  (A 12 kW 3 phase inverter is actually 3 x 4kW single phase inverters).
                  Participation is voluntary.

                  Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                  Comment

                  • GCE
                    Platinum Member

                    • Jun 2017
                    • 1473

                    #10
                    Originally posted by Dave A
                    Your 16 amp reading seems to be a sum of the current on all three phases.
                    You multiply by 1.73 when you are using the current for one of the 3 phases ... (and this assumes a balanced load).

                    Edit: Rather use the average current per phase for the calculation.
                    And perhaps 380 rather than 400 as they are running at 220V per phase.
                    (A 12 kW 3 phase inverter is actually 3 x 4kW single phase inverters).
                    The inverter readings added seem to show 16 amp total yet the multi meter reading on 1 phase is 16amp and it is balanced - all 3 phases show a 16amp draw/phase on each inverter making a total draw on the DB at 32 amp per phase after the parallel takes place

                    Comment

                    • GCE
                      Platinum Member

                      • Jun 2017
                      • 1473

                      #11
                      Originally posted by Dave A
                      Your 16 amp reading seems to be a sum of the current on all three phases.
                      You multiply by 1.73 when you are using the current for one of the 3 phases ... (and this assumes a balanced load).

                      .
                      which is what it is 16amp on one phase and it is balanced as it is 4 escalators with 3 phase motors , each escalator drawing 8 amps per phase , confirmed with tong test

                      Comment

                      • Derlyn
                        Platinum Member

                        • Mar 2019
                        • 1748

                        #12
                        From the 8A per phase reading that you get for each motor, that calculates to 3.68Kw/ph multiply by 3 = 11Kw.

                        Can you confirm if they are 11Kw motors ?

                        Ooops !!! a 5.5Kw motor draws approx 7,5A.

                        Can you confirm what size the motors are ?
                        That will confirm if the AC readings obtained with the tong tester are correct.

                        Comment

                        • GCE
                          Platinum Member

                          • Jun 2017
                          • 1473

                          #13
                          Originally posted by Derlyn
                          From the 8A per phase reading that you get for each motor, that calculates to 3.68Kw/ph multiply by 3 = 11Kw.

                          Can you confirm if they are 11Kw motors ?

                          Ooops !!! a 5.5Kw motor draws approx 7,5A.

                          Can you confirm what size the motors are ?
                          That will confirm if the AC readings obtained with the tong tester are correct.
                          Cant get to the motors - Have used 3 different tong testers in different makes as well and the logger - All 4 give the same readings
                          Last edited by GCE; 10-Jul-24, 03:56 PM.

                          Comment

                          • GCE
                            Platinum Member

                            • Jun 2017
                            • 1473

                            #14
                            These are 2 pics of the inverter screen running on grid in parallel
                            On the load side under one with a tong tester I get 25amps and on the other 14 amps


                            Comment

                            • Derlyn
                              Platinum Member

                              • Mar 2019
                              • 1748

                              #15
                              There are a million things going through my mind. So many questions.

                              Are you any closer to solving the mystery ?

                              Sounds as if there's power coming from somewhere else besides the batteries.

                              If there were panels involved then one could understand it, but without panels, it is a mystery.

                              Is the output of a 3ph inverter in a star or delta configuration?

                              Comment