Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I need to connect two buildings (approximately 500mm apart) with a 2.5mm Surfix cable. The cable will be suspended approximately 3.5 meters above the ground. To ensure the safety and integrity of the cable, I am considering placing it within a 20mm PVC conduit, which will be supported with a suitable structure.
Will it be sufficient?
Any insights or recommendations will be appreciated.
I need to connect two buildings (approximately 500mm apart) with a 2.5mm Surfix cable. The cable will be suspended approximately 3.5 meters above the ground. To ensure the safety and integrity of the cable, I am considering placing it within a 20mm PVC conduit, which will be supported with a suitable structure.
Will it be sufficient?
Any insights or recommendations will be appreciated.
SANS 10142 doesn't say much about aerial conductors other than
6.3.4.1
An aerial conductor shall be of a) hard-drawn copper, b) stranded aluminium, or c) composite construction, such as steel-cored aluminium.
6.3.4.2
A surge arrester shall be installed at each end of each aerial conductor circuit in an installation.
The arrangement, support and where required, insulation of an aerial conductor shall comply with the relevant statutory requirements.
I assume that what is meant by statutory requirements is local by laws, so it would depend on your locality and the laws of the area.
I'll stick my neck out and suggest that what you are planning to do is acceptable as long as the route does not cross any roads.
I would check the cable manufacturers instructions regarding surfix as an aerial installation. I'd suggest rather use steel conduit, not PVC for overhead or even unistrut with a lid if it's only half a meter between buildings, PVC conduit will sag over time and not look great a year from now. Personally I'd probably go with 2.5x3 SWA cable with unistrut to bridge the gap, the price difference would be negligable and it would be easier installation.
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.