So this happened to me yesterday 16/6/2024.
I was invited to a braai in Gonubie.
Whilst there, the host showed me his "beautiful" 8Kw Sunsynk inverter installation. ( His description )
At a quick glance it does look beautiful, but something jumped out at me. No labels on AC DB.
I pointed this out to him.
He asked if I could see any other defects so I made arrangements to go back this morning and have a more in depth look see and this is what I found.
1. The PV panels on the roof have not been bonded and earthed.
2. No earth spike for the PV panels.
3. No earthing cable has been pulled in between the panels and the inverter.
4. The surge arrestors in the DC combiner box have no earth connected making them
inoperable in the event of a surge.
5. The components in the AC control DB have not been labelled.
6. Neither the inverter input nor output have surge arrestors installed.
7. There is no “ Grid power on” indicator light or audible alarm fitted.
8. No bridging relay for neutral earth bonding during islanding mode has been installed.
( I created a mains power failure and showed him that the earth leakage will not work without it. )
9. Some fine stranded cable terminations do not have bootlace ferrules.
10. The supply earth wire on the inverter has no lug. Just twisted under a screw.
11. The batteries have not been bonded and earthed.
12. No CT coil has been installed on the grid incoming supply.
The installation was done and coc supplied by an electrical tester for single phase who is now "specialising" in solar installations.
The owner has requested that I supply a quote to bring the installation up to standard, which I am working on.
He has indicated that, no matter the cost, he is going to bring the culprit to book. I have advised him that I do not, as a matter of principle, get involved with these disputes, but at the same time have informed him of the steps he should take.
I was invited to a braai in Gonubie.
Whilst there, the host showed me his "beautiful" 8Kw Sunsynk inverter installation. ( His description )
At a quick glance it does look beautiful, but something jumped out at me. No labels on AC DB.
I pointed this out to him.
He asked if I could see any other defects so I made arrangements to go back this morning and have a more in depth look see and this is what I found.
1. The PV panels on the roof have not been bonded and earthed.
2. No earth spike for the PV panels.
3. No earthing cable has been pulled in between the panels and the inverter.
4. The surge arrestors in the DC combiner box have no earth connected making them
inoperable in the event of a surge.
5. The components in the AC control DB have not been labelled.
6. Neither the inverter input nor output have surge arrestors installed.
7. There is no “ Grid power on” indicator light or audible alarm fitted.
8. No bridging relay for neutral earth bonding during islanding mode has been installed.
( I created a mains power failure and showed him that the earth leakage will not work without it. )
9. Some fine stranded cable terminations do not have bootlace ferrules.
10. The supply earth wire on the inverter has no lug. Just twisted under a screw.
11. The batteries have not been bonded and earthed.
12. No CT coil has been installed on the grid incoming supply.
The installation was done and coc supplied by an electrical tester for single phase who is now "specialising" in solar installations.
The owner has requested that I supply a quote to bring the installation up to standard, which I am working on.
He has indicated that, no matter the cost, he is going to bring the culprit to book. I have advised him that I do not, as a matter of principle, get involved with these disputes, but at the same time have informed him of the steps he should take.