Sunsynk customer service

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Isetech
    Platinum Member

    • Mar 2022
    • 2274

    #1

    Sunsynk customer service

    I must say things are certainly improving. As I am sure you have read in the past, I have had nothing good to say about Sunsynk support, their technical support was bad.

    I found a magnetic (ferrite) ring inside the inverter box this weekend, while doing an installation. Something I have never seen inside the box before (or should I say never noticed). The ring is used to prevent interference. My question was do I have to install the ring, does tit affect the inverter warranty (really that is all that matters)?

    Logged into my Sunsynk plant list, click on top right corner (application center), then customer support and enter, 3 seconds and I got a response, typed in my enquiry and within 5 minutes the query was resolved.

    I am impressed.

    Anyone can use this support, customer or installer.

    If you use the app on the phone, go to me, tap application center, customer support, tap enter and type your query.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.
  • Andrew_van_Zyl
    Bronze Member

    • Mar 2022
    • 131

    #2
    Ya they have upped their service levels.
    Haven't come across a ferrite ring yet - what do they say one has to do with it?

    Comment

    • Isetech
      Platinum Member

      • Mar 2022
      • 2274

      #3
      It was found inside the Sunsynk inverter box last week, it is mentioned in the installer manual.

      It is used to reduce interference, you wrap the battery cable twice through the ring. I dont know how you would get 2 x 50 mm battery cables looped twice through the ring and still get it into the terminals inside the inverter.

      The small ring is for the BMS comms cable, same thing. just you wrap it 4 times.

      I have read of people experiencing noise on ham radios, maybe that would reduce the interference, I have never tried it.
      Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

      Comment

      • Isetech
        Platinum Member

        • Mar 2022
        • 2274

        #4
        I have a lot bad things to say about Sunsynk technical support, today I had to go to one of the sites I manage, due to a complete shutdown with an alarm.

        Because we haven't had load shedding for 23 days, I have made a few adjustments to all the sites, unfortunately one site had a major power problem in the area, so it has been off for a couple of days and we because haven't had any sun for a couple of days, the batteries dropped below the thresh hold. I made a few adjustments to get the system back on line, unfortunately that didnt work, including a factory reset, which also didn't work, resulting in a tech support call.

        Called technical support, got a ticket emailed with a couple of minutes, the call was transferred to a technician in SA. Gerrie ran through why the system would not switch on, gave me a ton of information about the batteries.

        Kudos to Sunsynk support, you guys have certainly improved your tech support.

        I give you 10/10 for the support today.
        Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

        Comment

        • Derlyn
          Platinum Member

          • Mar 2019
          • 1748

          #5
          Will I be doing myself a mischief buying one ?

          Comment

          • Derlyn
            Platinum Member

            • Mar 2019
            • 1748

            #6
            My previous post disappeared.

            I've heard from more than a couple of installers that they are going for Luxpower inverters. The motivation seems to be price.

            Will I be doing myself a mischief buying one ? 5Kw 10 grand.

            Comment

            • GCE
              Platinum Member

              • Jun 2017
              • 1473

              #7
              Originally posted by Derlyn
              My previous post disappeared.

              I've heard from more than a couple of installers that they are going for Luxpower inverters. The motivation seems to be price.

              Will I be doing myself a mischief buying one ? 5Kw 10 grand.
              I talk under correction - The Lux Power is an off grid inverter and so you do not have the advantage of "feeding back " within your grid to non essential loads with PV during the day when there is excess solar.

              So , the price is attractive short term , but long term savings it is better to go with a full hybrid that can feed essential loads and use excess solar to feed " your grid " for lack of a better terminology

              Comment

              • Derlyn
                Platinum Member

                • Mar 2019
                • 1748

                #8
                Thank you brother.

                I've also heard that here in our valley, there are clients with large solar systems who are so disillusioned with the tariff structure here that they have instructed their respective installers to set up the system so that it doesn't feed back.

                I'm going to dig a bit deeper to come up with figures as to why they would choose that option.

                I know so far that irrespective of the system size, 20A per phase is the maximum that is allowed to be fed back and the rebate is R1 / KWh.

                Comment

                • GCE
                  Platinum Member

                  • Jun 2017
                  • 1473

                  #9
                  Originally posted by Derlyn
                  Thank you brother.

                  I've also heard that here in our valley, there are clients with large solar systems who are so disillusioned with the tariff structure here that they have instructed their respective installers to set up the system so that it doesn't feed back.

                  I'm going to dig a bit deeper to come up with figures as to why they would choose that option.

                  I know so far that irrespective of the system size, 20A per phase is the maximum that is allowed to be fed back and the rebate is R1 / KWh.
                  There is feeding back to municipal grid and applying for net metering etc and then there is feeding back to your own grid only

                  When I refer to feeding back o your own grid - on the inverter we put tv,router , alarm , lights and a socket for charging - that will be essential load (UPS) and be battery backup when load shedding occurs .
                  Feeding back into your grid to supplement grid the solar will at least supply power to fridge , geyser , wash machine etc without actually loading the inverter

                  Where you are feeding back to your grid an overload on the grid side cannot damage the inverter as the inverter will only give out excess between the inverter and the CT that you place at mains
                  On the example below - Sun is capable of producing 3.32Kw - on an offgrid it will only feed battery and UPS load and you would be " wasting " the chances of using the other 750w of electricity - Because this is a true hybrid and can feed back onto his grid it allows the extra solar to feed fridges , oven , microwave etc without running the risk of overloading the inverter
                  the 40w from the grid is to stop the prepaid meter from tripping

                  Click image for larger version

Name:	Grid tie example .jpg
Views:	1
Size:	15.8 KB
ID:	266329

                  Comment

                  • Derlyn
                    Platinum Member

                    • Mar 2019
                    • 1748

                    #10
                    Thank you, brother.
                    I've still got a lot to learn about inverters. 👍👍

                    Comment

                    • Justloadit
                      Diamond Member

                      • Nov 2010
                      • 3518

                      #11
                      Originally posted by GCE
                      the 40w from the grid is to stop the prepaid meter from tripping
                      The 40W is also used for the inverter to identify that the grid is active and for synchronizing
                      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                      Comment

                      • GCE
                        Platinum Member

                        • Jun 2017
                        • 1473

                        #12
                        Originally posted by Justloadit
                        The 40W is also used for the inverter to identify that the grid is active and for synchronizing
                        Standard type setting that they come with is 20w - we find that we have to set to 40w for older prepaid and set to 80w for new conlog prepaids as when there is quick change in load the prepaid trips

                        We find on Tesla , even though feed back is not selected the sensitivity of the prepaid meters is that it trips - We have to put a load on the grid side to absorb the suddenly change

                        Comment

                        • Justloadit
                          Diamond Member

                          • Nov 2010
                          • 3518

                          #13
                          Originally posted by GCE
                          Standard type setting that they come with is 20w - we find that we have to set to 40w for older prepaid and set to 80w for new conlog prepaids as when there is quick change in load the prepaid trips

                          We find on Tesla , even though feed back is not selected the sensitivity of the prepaid meters is that it trips - We have to put a load on the grid side to absorb the suddenly change
                          Was not aware that one could program the minimum power on the Sunsync.
                          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                          Comment

                          • GCE
                            Platinum Member

                            • Jun 2017
                            • 1473

                            #14
                            Originally posted by Justloadit
                            Was not aware that one could program the minimum power on the Sunsync.
                            Cant get into Sunsync now but on the Deye it is under System work mode and called " Zero Export power"

                            Comment

                            • Derlyn
                              Platinum Member

                              • Mar 2019
                              • 1748

                              #15
                              Must apologise to Isetech for hijacking his thread but seeing that feeding back into "my" grid was explained, there's still something that I'm grappling with to understand.

                              Ok, so my db is split into essential and non essential. Inverter ( real hybrid ) feeds the essentials. Now any eccess power generated by the panels can be fed to the non essentials without loading the inverter.

                              My question is. How does the excess power from the panels (dc) get converted to 230vac and feed the non essentials without going through or loading the inverter ?

                              Comment