    Kitchen sink bonding

    Hi

    Bonding questions.

    1 .A stainless steel sink supported by a stainless steel frame and legs.It has pvc drain pipes and those flexible metal braided pipes feeding from the copper water supply to the sink mixer.

    2.What if my resistance reading to the sink is 0.2 Ohms or less.

    Must this sink be bonded?

    Thanks for all the previous informative discussions.


    Sent from my CPH2197 using Tapatalk
  • Derlyn
    Platinum Member

    • Mar 2019
    • 1748

    #2
    From where are you measuring 1,2 ohms ? Between the sink and what ?

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #3
      Sorry typo. 0,2 ohms.

      Comment

      • Gtfast
        Full Member

        • Apr 2016
        • 78

        #4
        I have not measured it yet.
        It would be between switch socket outlet cover and sink.


        Sent from my CPH2197 using Tapatalk

        Comment

        • Die sparky
          Full Member
          • Nov 2023
          • 25

          #5
          I believe if it is less than 7.7 Kohm to the earth terminal it needs to be bonded.

          Comment

          • Gtfast
            Full Member

            • Apr 2016
            • 78

            #6
            Thanks
            Where did you get this info from?


            Sent from my CPH2197 using Tapatalk

            Comment

            • Die sparky
              Full Member
              • Nov 2023
              • 25

              #7
              https://youtu.be/TFt3d77LujQ?si=YXW4slj0HgI-lLuh its not sans but how would one know when something is extraneous conductive?

              Comment

              • Gtfast
                Full Member

                • Apr 2016
                • 78

                #8
                Interesting.
                Thanks


                Sent from my CPH2197 using Tapatalk

                Comment

                • GCE
                  Platinum Member

                  • Jun 2017
                  • 1473

                  #9
                  You Tube can be a dangerous place to take information and regard it as gospel - Rather check against the actual regulations

                  Sans requires hot and cold water systems to be bonded and then also refers to everything within arms reach etc - So in short , I would say you need to test and make sure it is within 0.2ohm - It does not need to have a physical bonding strap

                  Extract from SANS 10142-1 ed 3.1 below

                  6.13 Bonding
                  NOTE 1 The aim of bonding is to bring all the bonded parts to the same electrical
                  potential.
                  NOTE 2 No external conductor is required if compliance with the requirements for
                  continuity can be proved by the test in 8.6.2.


                  6.13.2.2 Hot and cold water systems
                  Where the hot water system includes electric components and the water pipes
                  are of conducting material, hot and cold water systems shall be bonded
                  together and also be bonded to the earth continuity conductor system.

                  8.6.2 Continuity of bonding
                  Confirm the continuity of the bonding conductors between all exposed
                  conductive parts within arms reach (or see annex A) of each other. When a
                  test device or instrument is used, it shall have a supply that has a no‐load d.c.
                  or a.c. voltage of 4 V to 24 V, and a current of at least 0,2 A. In each case, the
                  resistance shall not exceed 0,2 Ω.

                  Comment

                  • Gtfast
                    Full Member

                    • Apr 2016
                    • 78

                    #10
                    Thanks
                    Something I was wrestling with.My brain hit a miss. If all bonding is correct .What about touch potential .One hand touches the correctly bonded pipes with feet on the ground.Current should always take the easiest way to earth via bonding and earth bar.Not through the person.