Quick one on SPDs... I tried to look at manuals but can't find.
What size conductors do we use ??
So if the SPD does not have an integrated fuse then we need to have Circuit breaker before the SPD, so I then assume if we use a 20A then 2.5mm is fine, but that's not a lot of amps.... So then we do 50A CB and 10mm cable and then I assume same size for the Earth ?
I can not find any info on what size cable and then what size circuit breaker.
Same goes with the N E bridge on the other thread... What size relay/ contactor and what's size CB ?
Sent from my CPH2197 using TapatalkComment
-
Quick one on SPDs... I tried to look at manuals but can't find.
What size conductors do we use ??
So if the SPD does not have an integrated fuse then we need to have Circuit breaker before the SPD, so I then assume if we use a 20A then 2.5mm is fine, but that's not a lot of amps.... So then we do 50A CB and 10mm cable and then I assume same size for the Earth ?
I can not find any info on what size cable and then what size circuit breaker.
Same goes with the N E bridge on the other thread... What size relay/ contactor and what's size CB ?
Sent from my CPH2197 using Tapatalk
If your CB is SP domestic 80Amps then that should protect most surge arrestors .
Relay size - same story - normal rules apply - If you have a 5Kw inverter the rating would be at least 20Amps with a surge of 7Kw on a 40 Amp CB protection on incomer and 20 Amp or 32 on output
Max PSSC is equal to Max Surge - rate accordinglyComment
-
The AUS-IoT Monitor (LoRa system) for electricity can be useful to prevent/reduce spikes. We can program the electricity meters in a complex to switch on in phases instead of all the units at the same time. That seems to work well for our customers.
[ATTACH=CONFIG]8670[/ATTACH]Comment
-
The AUS-IoT System allows Managing Agents to manage their utilities (water, gas & electricity) on a dashboard and an Android app for the tenants. Meters are read online and alerts for leaks and faults are sent via the system and email.Excellence is not a skill; its an attitude...Comment
-
Hi all a few months ago my. Customer calls and says big bang on db .I take voltage reading and find
380 volts between l and n instead of 230v
Neutral gone on trafo.will surge protector have helped
Because the earth leakage. And geyser timer
Didn't work any more?Comment
-
I also had one that the surge arrestors started smoldering due to the current that it was pulling down to earthComment
-
I dont believe people realise how dangerous it is when the neutral cable/bar is stolen, not only from the voltage but also a fire hazard. It is EXTREMELY dangerous when the neutral is removed.Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.Comment
-
In a single phase domestic installation we normally fit a CBI 2 pole arrestor. This will trip if it gets a 275v input either on neutral or live incoming.
So in your case i would like to know if this device will trip.
I always try to get the customer to also put external plug in surge arrestors especially on individual items like TV, computer and expensive appliances.Comment
-
This is why here in the Cape we have to have our earthing spot on, all installations require their own earth spikes/mats and must have the correct readings. The Incoming N is linked to the Earth spike at the entry point in meter boxComment
-
Good day
I currently import surge protection units, i have tried contacting the insurance companies to make an offer for these devices and nobody is interested.
It just doesnt make sense to me. They could save millions on surge claims.
I have been testing my units for roughly 8 months now and they work perfectly.
Keep well.Comment