6.14.1.6 In a lighting circuit, a luminaire may be fed from a socket-outlet on a
wall (that may be unswitched), provided that the socket-outlet
a) complies with SANS 164-3 or SANS 164-2-1 (partially dedicated
socket-outlet), Amdt 1
b) is protected by earth leakage protection, except in the case where
SANS 164-2-1 (partially dedicated socket-outlet) socket outlets are fitted,
Amdt 1
6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
6.6.3.3.3. Amdt 1
6.16.3.3.3 The stove connections may be wireddirectly between the isolator
and the stove terminals, by means of a flexible arrangement, which are
mechanically secured and be terminated on either end. When the stove is
removed, the final section of hard wiring to the stove terminals has to be
removed and made safe. Amdt 1
7.16.3 Voltage drop
The designer of the distribution system shall select the components in order
to ensure a minimum voltage drop over the system, which will allow for the
voltage drop over the entire installation, which is the distribution system, not
to exceed the 5 % of the circuit nominal voltage (see 6.2.7) and maintaining
the overall voltage requirements in 5.4.2. Amdt 1
(3)
Table 6.2.8 (b)
(h)
6.14.1.6 In a lighting circuit, a luminaire may be fed from a socket-outlet on a
wall (that may be unswitched), provided that the socket-outlet
a) complies with SANS 164-3 or SANS 164-2-1 (partially dedicated
socket-outlet), Amdt 1
b) is protected by earth leakage protection, except in the case where
SANS 164-2-1 (partially dedicated socket-outlet) socket outlets are fitted,
Amdt 1
6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
6.6.3.3.3. Amdt 1
6.16.3.3.3 The stove connections may be wireddirectly between the isolator
and the stove terminals, by means of a flexible arrangement, which are
mechanically secured and be terminated on either end. When the stove is
removed, the final section of hard wiring to the stove terminals has to be
removed and made safe. Amdt 1
7.16.3 Voltage drop
The designer of the distribution system shall select the components in order
to ensure a minimum voltage drop over the system, which will allow for the
voltage drop over the entire installation, which is the distribution system, not
to exceed the 5 % of the circuit nominal voltage (see 6.2.7) and maintaining
the overall voltage requirements in 5.4.2. Amdt 1