7.12 Alternative supplies
Collapse
X
-
I went and had a look at my generator and did a few continuity tests.
The tank is isolated from the frame.
the flex conduit between the alternator and socket is PVC ...
Then I thought surely the socket outlet has an earth from the alternator which is also mounted on the outer metal frame ... no continuity ... it seems the earth from the alternator is also isolated from the metal frame ... using a plastic socket outlet.
Thanks for the lesson ... this is what I love about this forum ... no matter how much you think you know ... there is always something to learn and you might see something or do something in a manner which you think is right ... but you might have been doing it wrong or just not seen it from another angle.
What we can learn from this ... never earth the socket to the frame of the generator on a VOV construction site generator.
Which now has me thinking about the other generators which We have connected to premises ... if the generator is not a VOV then how as these unit make safe and what happens if you bond the earth to the frame?Comments are based on opinion...not always facts....that's why people use an alias.Comment
-
Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .
6.1.6 The neutral conductor shall not be connected direct to earth or to the
earth continuity conductor on the load side of the point of control except as
allowed in 7.16.4.
You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.
The reason behind the reg is to prevent fires and I will take an extreme case as an example.
My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.
If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
That earth neutral current flow could be as high as 200Amp on an imbalanced load.
That is the though process for that particular regulationI should have thought of the PEN fault. I really appreciate it !
Sent from my SM-N960F using TapatalkComment
-
I would say No! Consult the battery or inverter manufacturer.
The Neutral of the AC side of the inverter is derived from the battery from a bridge type electronics, so in effect, the negative side of the battery and PV panels are effectively connected to the Neutral of the AC out via a Diode/FET.
Joining this to earth would damage the inverter.
To add a little bit more here. Whilst the Neutral is connected to the negative of the PV panels and battery, it is not a permanent connection, but rather a high speed switching, in which the Neutral of the AC output is effectively alternated On/Off between the battery/PV positive and negative terminals.
Only in the case that the battery/PV are isolated from the AC output may the DC negative side be earthed. However I doubt that they are isolated, as this would increase the cost and physical size of the inverter by introducing an isolating transformer.so much to learn and technical items to learn. We do follow manufactures but I like to know why things are done in a certain way. Some of the older gents I talk to don't know as its new technology to them too. Really appreciate your reply, thank you !
Sent from my SM-N960F using TapatalkComment
-
Ok so I phoned a friend ... now I am pissed off because a I stalled purchasing ed 3 ... edition 3.1 was launched 2 weeks ago and by the way apparently there are many changes in the new edition and it still doesnt include the other draft that is still in draft ...
I also need to get the NRS 097 code to understand solar installations.
I enquired about the functional earth and that kind of stuff and as usual ... its never just as simple as we think
Sent from my SM-N960F using TapatalkComment
-
It might be a good idea to read this document if you planning to do a solar install
Comments are based on opinion...not always facts....that's why people use an alias.Comment
-
What is the use thereof ? When should it be used ?
DerekComment
-
7.12 Alternative supplies
NOTE Alternative supplies include but are not limited to low-voltage generating sets,
photovoltaic (PV) installations, gas generators, diesel generators, wind turbines and
hydropower plant.
7.12.1 General
7.12.1.1 Subclause 7.12 applies to an installation that incorporates
alternative supplies intended to supply, either continuously or occasionally, all
or part of the installation with the following supply arrangements:
a) supply to an installation or part of an installation which is not connected to
the main supply of a supplier;
b) supply to an installation or part of an installation as an alternative to the
main supply of a supplier; and
c) appropriate combinations of the above.
NOTE 1 Requirements of the supplier should be ascertained before any alternate
supply is installed in an installation connected to the main supply of a supplier.
NOTE 2 This part of SANS 10142 does not cover the generation plant, integration and
synchronising requirements of an alternative supply operating in parallel with the main
supply to an installation.
Grid tied or Hybrid inverter and solar systems.
The item covered in red ... something which I have noticed people are turning a blind eye ... they are aware of the consequences of the installation and the type of meter installed.
The question is going to be who will be held liable for the penalties and or investigation into the usage ... will the inspector who signed the COC be responsible or the owner using the electricity. How would they calculate the estimated usage ... will they fine you will you be liable from the date on the COC ? I dont think people signing COC's understand the implications of signing the COC.
People it is not that difficult to work out how much power you are pushing back into the grid ... especially if you have a remote monitoring system.
2 thing you gonna need to be aware of ... the date on the COC or invoice date for the installation and remote viewing data.Comments are based on opinion...not always facts....that's why people use an alias.Comment
-
Morning
So if we add a generator, change over switch and all that, do we still need to contact the supplier ?
My view is that as there is a change over there is no backfeeding thus no need to contstc supplier.
Keen to find out more in this.
Also what i need to find more on but may do annew thread is with PV installs and registration of them and then if not used to backfeed at all then must it still be registred.
Sent from my SM-N960F using TapatalkComment
-
Morning
So if we add a generator, change over switch and all that, do we still need to contact the supplier ?
My view is that as there is a change over there is no backfeeding thus no need to contstc supplier.
Keen to find out more in this.
Also what i need to find more on but may do annew thread is with PV installs and registration of them and then if not used to backfeed at all then must it still be registred.
Sent from my SM-N960F using TapatalkComments are based on opinion...not always facts....that's why people use an alias.Comment
-
OK cool, i did not know that... thanks for sharing !
Will get onto learning more
As a start... so if we connect the genny on the consumer side mains in, I.E at the top of breaker in Main DB, is that still considered supplier mains ? My thought process now is that that would be consumer mains as on the consumer side. (Over simplified connection but just to get point across)
Not trying to dodge phoning council but dealing with council does not fill me with joy hahaha.
Also just want to properly understand.
Sent from my SM-N960F using TapatalkComment
-
OK cool, i did not know that... thanks for sharing !
Will get onto learning more
As a start... so if we connect the genny on the consumer side mains in, I.E at the top of breaker in Main DB, is that still considered supplier mains ? My thought process now is that that would be consumer mains as on the consumer side.
Not trying to dodge phoning council but dealing with council does not fill me with joy hahaha.
Also just want to properly understand.
Sent from my SM-N960F using Tapatalk
38. Standby supply
No person shall be entitled to a standby supply of electricity from the Municipality for any premises having a seperate source of electricity supply except with the written consent of the Municipality and subject to terms and conditions as may be laid down by the Municipality.
39. Consumer's emergency standby supply equipment
1) (1) No emergency standby equipment provided by a consumer in terms of any Regulations or for the consumer's own operational requirements shall be connected to any installation without the prior written approval of the Municipality. Application for such approval shall be made in writing and shall include a full specification of the equipment and a wiring diagram. The standby equipment shall be so designed and installed that it is impossible for the Municipality's supply mains to be energized by means of a back feed from such equipment. The consumer shall be responsible for providing, installing and maintaining all such protective equipment.
2) Where by special agreement with the Municipality, the consumer generating equipment is permitted to be coupled to, and run in parallel with the Municipality's supply mains, the consumer shall be responsible for providing, installing and maintaining all the necessary synchronizing and protective equipment required for such safe parallel operation, to the satisfaction of the Municipality.
There is more but I'm tired of typing.
Suggest you check out the by laws in the area that you are working in.
Peace out ... Derek
edit: @ Dylboy, the top of your main breaker in the DB is supply side. The bottom of your main breaker is consumer side.Comment
-
Attached is BCMM By law.
38. Standby supply
No person shall be entitled to a standby supply of electricity from the Municipality for any premises having a seperate source of electricity supply except with the written consent of the Municipality and subject to terms and conditions as may be laid down by the Municipality.
39. Consumer's emergency standby supply equipment
1) (1) No emergency standby equipment provided by a consumer in terms of any Regulations or for the consumer's own operational requirements shall be connected to any installation without the prior written approval of the Municipality. Application for such approval shall be made in writing and shall include a full specification of the equipment and a wiring diagram. The standby equipment shall be so designed and installed that it is impossible for the Municipality's supply mains to be energized by means of a back feed from such equipment. The consumer shall be responsible for providing, installing and maintaining all such protective equipment.
2) Where by special agreement with the Municipality, the consumer generating equipment is permitted to be coupled to, and run in parallel with the Municipality's supply mains, the consumer shall be responsible for providing, installing and maintaining all the necessary synchronizing and protective equipment required for such safe parallel operation, to the satisfaction of the Municipality.
There is more but I'm tired of typing.
Suggest you check out the by laws in the area that you are working in.
Peace out ... Derek
edit: @ Dylboy, the top of your main breaker in the DB is supply side. The bottom of your main breaker is consumer side.
Also saw the pollution pdf so got that too for some reading.
Really appreciate it all gents, thank you.