I must comment on the main switch.
I am not sure about different parts of the country but in KZN east coast the meter box has a circuit breaker feeding the installation which offers protection for the supply cable. Therefore any combined DB load over the circuit breaker rating (normally 60A for a domestic installation) the meter box circuit breaker will trip. By having a mains circuit breaker installed at the DB all that will be accomplished is that it may be more convenient to have the breaker trip at the house rather than the suppliers side. However, having the switch at the DB doesnt always mean it will trip there and not at the suppliers side.
As far as I am aware SANS does not require another mains circuit breaker at the DB, only a double pole disconnector.
I also noticed that there is a surge arrester installed - not a requirement but may be beneficial.
I am not sure about different parts of the country but in KZN east coast the meter box has a circuit breaker feeding the installation which offers protection for the supply cable. Therefore any combined DB load over the circuit breaker rating (normally 60A for a domestic installation) the meter box circuit breaker will trip. By having a mains circuit breaker installed at the DB all that will be accomplished is that it may be more convenient to have the breaker trip at the house rather than the suppliers side. However, having the switch at the DB doesnt always mean it will trip there and not at the suppliers side.