Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I have recently had to COC a socket outlet circuit in an existing installation. (The current one is a single 32A single phase industrial socket). This socket is the backup to server equipment via a UPS feed via a 20A 5KA S/P C/B. The problem I have is that the KA test and earth loop impedence test cannot be performed because it is fed from a UPS.
How do you complete the COC in these circumstances.
Yes I thought of that but the feed DB to the socket outlet is in a server / control room and is part of a large refinery. The DB (floor to ceiling 6 door cabinet) supply comes from another location where the UPS is. The whole DB is on UPS and as you can imagine there is no chance of them switching the main UPS on bypass so the test can be performed.
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.