Does a stove need to be on an earth leakage?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • DieterT
    Bronze Member

    • Oct 2014
    • 126

    #46
    What Lionels said.

    That electrician you got sounds to be very lazy.
    There is a thing we call fault finding. It's tripping so lets go and find out the origin of the problem.
    Look if your oven is broken, old and looks the part to be replaced, then by all means do so. I would look firstly at the elements, those who tend to get a bit of moisture / splatter from baking & cooking. Do insulation tests on them and move on from there. It could even be the supply cable to the oven that is the problem.

    We had a client which complained that as soon as they used the iron the earth leakage would trip.
    So they replaced the iron. About 4 irons later, each more expensive than the last, they asked that we come to separate the circuits on the house cause with original installation they wired everything underneath earth leakage. So creating a essential side and non-essential side, everything still under earth leakage, the iron tripped a earth leakage again. Luckily not the rest of the house, fridge/freezer etc. cause of the separation.

    So we went to do fault finding and eventually after making sure nothing is plugged in and having done an insulation resistance test, found there was a problem on the circuit. We then disconnected all the plug sockets and found that the one where the iron was plugged into had moisture in the back, possibly damp rising (and the rest of the sockets on the same outside wall) Luckily the wire supplying the circuit was fine.
    So yes, you might change the oven, but the problem could also be with the rest of the circuit feeding the oven. Good place to start, the elements and then work your way back to the origin of the supply.

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #47
      Originally posted by phillyza
      ...Yesterday I did a test and switch off all other circuit breakers except the mains, earth leakage and the oven. Just to eliminate other influences.
      This wouldn't eliminate all other influences unless the circuit breakers are double pole (SP+N).


      Originally posted by phillyza
      I had an electrician out at our place and explained to him what happens and he suggested (without testing anything) just to buy a new oven. He indicated that it can be the switch or the thermostat or the element and we can replace one by one but we might still have the problem and its just easier to replace the oven.
      Not sure why he wouldn't do some tests to localise the fault and prove the supply circuit is okay. He's not done his job so I hope he didn't charge you.

      Yes, the fault could lie with any of the components mentioned but it's highly unlikely. The most likely candidate by far is the actual element but some basic testing would be the way to go before blindly replacing parts or the entire oven without knowing for sure where the fault is.

      Originally posted by phillyza
      No I need a second opinion as the 2x tripping while warming up don't really justify getting a new oven, unless I'm wrong? I understand the problem is that somewhere in the circuit there is current leaking and can cause electrical shock, but can't this be traced to the exact component causing the problem?

      Your assistance would appreciated.
      Yes it can be traced by any competent sparky who isn't in such a rush or so lazy he doesn't want to run some tests.
      _______________________________________________

      _______________________________________________

      Comment

      • Ndzondie
        New Member
        • Aug 2017
        • 4

        #48
        Do i need to connect my stove from protected neutral or from unprotected and why?

        Comment

        • Sparks
          Gold Member

          • Dec 2009
          • 909

          #49
          The stove circuit is not required by law to have a protected supply. Provided you have a good earth connection it is safe to disconnect it from the earth leakage. I would however suggest you rather determine which element is faulty and just replace that one yourself. Because the fault is in all likelihood a hairline crack as already explained you can determine which one is faulty by process of elimination. Switching them on one by one. If your oven has preheat it will switch on more than one element so do not use that setting.

          Comment

          • hislordship
            New Member
            • Dec 2017
            • 2

            #50
            Oven Tripping SOMETIMES

            Here is an interesting situation for you.
            My oven bake element started tripping earlier this year. Bake element. I got the replacement and fitted it. Worked for a while and started tripping again. But only randomly. Not every time. Plus when it trips it will work immediately again and only trip later.

            I thought it must be the top bake/grill combination one this time.
            Did some testing by disconnecting and running them etc. Turns out it is the bake one again, hardly used.

            But during my testing I tried running the oven off an extension cable from my garage DB (3 phase E/L 30mA) and it never tripped.
            House DB was the old Heinemann 3 phase 20mA sensitivity type.

            There was also one week here where the whole neighbourhood was on low voltage (220v down to 200v over the normal 240v to 230v range, fault was eventually found to be Brightwater Commons when the whole area blacked out one night). During this time the oven didn't trip the house E/L once.

            So knowing the E/L was old I changed it yesterday to a new 3 phase 30mA one. More for safety than for the oven issue (it wasn't always disconnecting all phases when it tripped).
            Oven still tripping the house board last night. Got the extension out and back to garage DB and it was fine.
            Tested voltage at oven terminals on house board. 240v.
            On different phase from garage board the voltage over the extension dropped to 220v at oven terminals.

            So this morning some more tests.
            Removed oven earth and tested earth to oven chassis voltage when hot. 115v. Touched earth wire to oven chassis and trip.

            I tried a hard wiring to the garage board with a temp cable.
            Finally the garage board tripped!

            It seems the element will work fine as long as the voltage goes no higher than 220v!
            But it is definitely faulty so must be changed AGAIN this year.

            Just posting this for your interest because it is such a strange turn of events.

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4946

              #51
              Originally posted by hislordship
              ............But during my testing I tried running the oven off an extension cable from my garage DB (3 phase E/L 30mA) and it never tripped.
              House DB was the old Heinemann 3 phase 20mA sensitivity type.
              Is the house DB the main DB? Is the 3-phase earth leakage breaker the 'main breaker'?


              Originally posted by hislordship
              So this morning some more tests.
              Removed oven earth and tested earth to oven chassis voltage when hot. 115v. Touched earth wire to oven chassis and trip.
              If you've got a known tripping fault on an appliance why would you disconnect the earth wire then put power on it and attempt to do live tests? This is dangerous. On top of that the tests you were doing are not relevant and their results are likely to be misleading. Firstly with a stove or oven there's highly likely to be parallel paths to earth, secondly the voltage you measured would be highly likely to vary wildly depending on the input resistance of the particular voltmeter you're using.

              If you suspect you've got a faulty element why don't you just disconnect and IR test the element with a mega tester at 500v? You can't accurately localise a fault by using the earth leakage breaker instead of the correct test equipment, you're just going to run yourself around in circles...... I can state with a high degree of certainty that if there's an earth leakage fault on an element it won't make any difference to the likelihood of the earth leakage breaker tripping if the supply voltage is 220v or if it's 240v.
              _______________________________________________

              _______________________________________________

              Comment

              • Sparks
                Gold Member

                • Dec 2009
                • 909

                #52
                IR test is the only way to say as Andy said, but not just the oven element. The oven itself could have a wire causing it, it could also be one of the stove plates, depending on the switches as there is a common neutral throughout the appliance.

                Comment

                • hislordship
                  New Member
                  • Dec 2017
                  • 2

                  #53
                  I posted my findings not for the benefit of being told how to do or not do something.
                  I may not be a registered electrician, but my knowledge of electricity and wiring standards is far better than what I have seen done.
                  I have 24 years of experience with electricity, so I know my TT from my TN-C-S (and missing neutral issues), my single phase from my three phase, my cable sizing etc. Heck, I told City Power about the voltage issue I described a week before the actual fault showed up. I told them to check their transformers etc for the cause.


                  In answer to the questions:

                  The house and the garage DBs are independent of each other. Wiring runs as follows (large property):

                  METER DB FEED TO MAIN DB (NEXT TO METER DB AT THE SIDE OF HOUSE)

                  MAIN DB [NO E/L] FEEDS
                  (1) SWIMMING POOL DB
                  (2) HOUSE DB
                  (3) GARAGE DB
                  (4) BURGLAR ALARM FLOODLIGHT SYSTEM [ONLY SINGLE PHASE BOARD]
                  [1-4 ABOVE ARE E/L BOARDS]

                  (1) FEEDS ADDITIONAL WORKSHOP D/B
                  (2) FEEDS ENTERTAINMENT ROOM DB AND BOREHOLE DB
                  (3) FEEDS STAFF ROOM DB


                  My use of removing the earth was to confirm 100% that the element is faulty which it has, and also to try to find why it would trip at certain voltages and not others.
                  I don't possess an insulation tester, as mentioned I am not an electrician as occupation.

                  The stove doesn't trip when using any of the plates, the warmer drawer or when using the grill option (top of oven, dual element).
                  Only the normal bake oven trips the power. So it must be either the new bottom bake element or the smaller of the two on the top element (around 20 years old).

                  As stated, the element doesn't trip consistently, so difficult to run it to see which on trips. Hence disconnecting the earth wire. This showed up the leakage to the chassis. On disconnecting the bottom element, the leakage disappeared.
                  PROBLEM SOLVED (also eliminates the top element as there was now NO leakage with it still connected).

                  I forgot to mention, on switching the oven on (without earth), the leakage shows up immediately, but at a much lower voltage (8v or so). it gradually rises as the element heats (obvious). BUT touching the earth to the chassis causes no trip 90% of the time, even when reading 115v chassis to earth. I tried touching it back 10 times, and only once did it trip. Did this mostly out of curiousity.

                  Yes removing the earth is not recommended, but I can tell you that the appliance was still on earth leakage, and also that no on else was allowed near the thing, even pets. I am very careful, excessively so. There was no risk to me at any point. No touching the chassis, no touching any of the wires directly.


                  Regardless of what you think, I can guarantee you the element NEVER trips at 220v or below. Any voltages above that and it will start tripping. If you don't believe me, you are welcome to the element to conduct tests. Collect from me in Randburg.

                  Why I posted this in the first place? To let everyone know that such an odd situation can arise. Not to find the problem. I've done that.
                  Also not to be sermonised on my methodology.
                  Remember, I didn't correct your incorrect use of it's (abbreviation of it is) vs its (possessive) and there's (there is) when you mean there are, i.e. as a plural.

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4946

                    #54
                    Originally posted by hislordship
                    .....Why I posted this in the first place? To let everyone know that such an odd situation can arise. Not to find the problem. I've done that.
                    Also not to be sermonised on my methodology.
                    I'm afraid we're going to have to agree to disagree on several points here and I can understand why you might see it that you're a victim of sermonising or your competence is being questioned but that isn't my objective.

                    The problem I had was that you've posted your fault finding endeavours as a fait accomplis and as something of a tutorial or reference for future readers on a public forum. The tests you've done are inconclusive but far more importantly, the minute you disconnected the earth wire and made the appliance live, they crossed the line and bacame dangerous. On a personal level I can't and never will be able to walk on by and not offer what I'd hope is a balanced reply to highlight hazardous practices and deter future casual visitors to the forum from believing that this may be acceptable practice and from doing the same.

                    Originally posted by hislordship
                    My use of removing the earth was to confirm 100% that the element is faulty which it has, and also to try to find why it would trip at certain voltages and not others.
                    I don't possess an insulation tester, as mentioned I am not an electrician as occupation.

                    The stove doesn't trip when using any of the plates, the warmer drawer or when using the grill option (top of oven, dual element).
                    Only the normal bake oven trips the power. So it must be either the new bottom bake element or the smaller of the two on the top element (around 20 years old).

                    As stated, the element doesn't trip consistently, so difficult to run it to see which on trips. Hence disconnecting the earth wire. This showed up the leakage to the chassis. On disconnecting the bottom element, the leakage disappeared.
                    PROBLEM SOLVED (also eliminates the top element as there was now NO leakage with it still connected).

                    I forgot to mention, on switching the oven on (without earth), the leakage shows up immediately, but at a much lower voltage (8v or so). it gradually rises as the element heats (obvious). BUT touching the earth to the chassis causes no trip 90% of the time, even when reading 115v chassis to earth. I tried touching it back 10 times, and only once did it trip. Did this mostly out of curiousity.

                    Yes removing the earth is not recommended, but I can tell you that the appliance was still on earth leakage, and also that no on else was allowed near the thing, even pets. I am very careful, excessively so. There was no risk to me at any point. No touching the chassis, no touching any of the wires directly.
                    In this post I've quoted you've spent the majority of it justifying a method of testing that is blatently dangerous and should never be done under any circumstances. There is no justification. 'Careful' isn't enough ....even someone who is trained and has the appropriate experience and equipment to work live would still identify and assess the risks for every stage of every job and then have a pre planned strategy for effectively managing them.

                    You've also reinforced a common misconception when you imply above that working live isn't so bad because there was still an earth leakage breaker to protect you. If you understood how an earth leakage circuit breaker works you'd know how dangerous that assumption is. It's not the first time I've seen statements like that so I'm going to give you some facts;

                    Click image for larger version

Name:	index.png
Views:	1
Size:	5.5 KB
ID:	265419
                    • The electrical supply is 50 Hz which means there's 50 complete cycles per second.
                    • Each cycle has full voltage twice, once in the positive and once in the negative hence the voltage is at its full value 100 times per second (every 10 milliseconds).
                    • An earth leakage circuit breaker is considered fully functional if it trips in 200 milliseconds for a 30mA fault.
                    • An earth leakage circuit breaker is considered fully functional if it trips in 40 milliseconds for a 150mA fault.
                    • An earth leakage circuit breaker is considered fully functional if it trips in 40 milliseconds for any leakage fault greater than 150mA.

                    Earth leakage circuit breakers are great for detecting potentially dangerous faults and disconnecting the circuit before someone gets a shock by tripping.
                    If you're the only path to earth because you've disconnected the earth wire and you've made direct contact with something that's live then a massive fault current can flow through you for 40 miliseconds meaning you get a full voltage shock 4 times before the earth leakage disconnects....and that's assuming it's working correctly. There's a very high likelihood of serious injury or death. Earth leakage breakers are only considered as supplementary protection (not primary protection) in the electrical regs for good reason.


                    Working on live circuits or appliances is unacceptably risky even for experienced electricians, disconnecting the earth wire first and then working live is even worse, downright reckless in fact.
                    Please don't do it, ever.
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • Festi
                      New Member
                      • Jan 2018
                      • 5

                      #55
                      Good day

                      I have a strange stove EL problem. When using a certain plate on the stove, we tend to set it to max and turn it down once the cooking temp is reached.
                      From time to time when 'switching down', it trips the EL. Max is '9', this trip happens even if the switch is set to 8.

                      A good few years ago I had the same issue in another house, when I had an electrician out he said the stove earth did not need to go through the EL and made the changes. As far as I knew at the time, the stove was still earthed, just not through the EL.

                      Am I sitting in the same situation?

                      Comment

                      • Festi
                        New Member
                        • Jan 2018
                        • 5

                        #56
                        Just a bit more info - when the switch is on '9', the switch clicks, and clicks again when setting to '8'.

                        Problem does seem to be more prevalent when any other plate is also on. although not always the case.

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4946

                          #57
                          Is it the spiral type or the solid heating plates?
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • Festi
                            New Member
                            • Jan 2018
                            • 5

                            #58
                            Morning Andy

                            Solid plates. switches turn like a volume control - click to start, smooth up to 8, then click onto 9. It's when turning from 9 down that the ELS trips. so from the MAX click.

                            Comment

                            • AndyD
                              Diamond Member

                              • Jan 2010
                              • 4946

                              #59
                              It's a bit odd, I thought the stoves with spiral plates had the type of temperature controller you describe and the stoves with solid plates click between every different setting. Also, don't the solid plate controls only have 5 or 6 temperature settings?

                              Can you attach a photo please?

                              Maybe one of the domestic sparkies can give you better info than me, it's not the kind of thing I usually work on so I'm not so familiar with it.
                              _______________________________________________

                              _______________________________________________

                              Comment

                              • Festi
                                New Member
                                • Jan 2018
                                • 5

                                #60
                                Thanks Andy

                                I did speak to Sparky, he suggested there could be a fault with the plate/s. I do not suspect the EL, this was replaced already, was very finicky when we had bad weather. After speaking to another electrician about this issue he suggested I get the EL changed then, the brand was a very fong kong type.

                                The stove we have is an AEG hob, all 4 plates work the same way - 0 clicks and then smooth up to 8, clicking to 9 (max) and then clicking when turning back to 8 and lower.

                                Switch are located on the oven.

                                Comment