So you do an inspection for COC.
You find an aircon circuit wired with 1.5mm wire protected by a 20A breaker. Problem.
Now you have
@ Leonsparky. Most inverters have a dedicated output to energize an external relay for neutral earth bonding during islanding mode, so I do not agree
Derlyn 04-Oct-24, 07:36 AMIf it is secured, it is a fitting part of the installation. if you deem that everything is not part of the coc if you plug it out, you can wire the entire
Leonsparky 03-Oct-24, 10:06 PM
Aircon circuit. Conductor and breaker size ?
Think couple of more questions before giving a definite answer
GCE Yesterday, 09:07 AMWhat is start up current , has the aircon maybe been changed to an inverter