Thread: Testing live installation

  1. #11
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I prefer to measure the PSCC, calculations can give very different figures to actual measurements.
    _______________________________________________

    _______________________________________________

  2. #12
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    I prefer to measure the PSCC.
    When you aren't allowed to switch off the main switch?

  3. #13
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    I measure at each control panel with 2 different loop testers and reading well within limits. The earth readings were very very low (the panels are side by side with SWA cables and separate earths and the whole structure is metal). I checked the bonding by the main panels, plenty of it but the with the size of the structure its hard to trace the bonding. I did a fly lead test to many metal parts of the machines and the structure and my Fluke 1653b and it alway read 0.01 ohms from local sumains. Its one big lump of earth metal. The only thing keeping the earth fault currents and PSCC down is the length of run of the conductors (100+ meter runs) but the cables are very oversized for there designed load so volt drop was minamal.
    The baggage handling company is only responsible for the protective device from the sub main to there panels which is the only part they are concerned about.

    Took the new Flir E4 for a spin whilst the panels were on full load. The only sign of any heat was from the contacter coils. Nothing to worry about

    How ever at a very good customer house my guys were doing a favour job at, just moving a pool pump housing, we had an incident. When dinner time came round and the oven was on, washing machine spinning, geyser was on we noticed that hot cable smell. Pointed the Flir at the DB to find the main cable was running at 180 degrees. Went to tell the client we urgently needed to switch off the power. Just as i got back to the board BoooooM!!! cable had melted through and touched down to earth. The customer confessed to trying to temporarily connect a generator to the board. He hadn't put the cable back in the right side of the terminal, feels tight with a screw driver but its not tight on the cable. I like the new thermal camera and the MSX feature is pretty nifty.

  4. #14
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Dave A View Post
    When you aren't allowed to switch off the main switch?
    Yes, I have a tester that performs PSC (L-E) + (L-N), ZE (Zdb), ZN, ZL etc as a live tests. A good investment for a couple of grand.
    _______________________________________________

    _______________________________________________

  5. #15
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    Yes, I have a tester that performs PSC (L-E) + (L-N), ZE (Zdb), ZN, ZL etc as a live tests. A good investment for a couple of grand.
    Perhaps we're missing each other.

    If the installation is live and running behind the main switch, and you're testing the PSC at the main supply point, doesn't the running installation affect the accuracy of the PSC test reading at the main switch?

  6. #16
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    No, the load the installation is under at the time of test shouldn't have any noticable effect on the live PSC or PEFC result taken at the point of supply.
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    Dave A (29-Jul-14)

  8. #17
    Full Member
    Join Date
    Feb 2014
    Location
    Fish Hoek
    Posts
    55
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Up your public liability insurance and sign it off.
    Apparently there is nothing that cannot happen today.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Live entertainment in Durban
    By MGM in forum General Chat Forum
    Replies: 0
    Last Post: 05-Feb-13, 07:49 PM
  2. Testing an exisitng installation without power
    By ians in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-12, 09:43 PM
  3. Testing an installation with more than 5 installations
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 03-Sep-12, 07:45 PM
  4. games for windows : Live
    By twinscythe12332 in forum Technology Forum
    Replies: 7
    Last Post: 30-Jun-10, 11:05 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •