Thread: 2 zone under floor heating thermostat

  1. #1
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts

    2 zone under floor heating thermostat

    Hi
    I went to customer who has under floor heating where the thermostats and double pole isolators were causing problems. 2 had burnt out one was busy in the process of melting (i can smell burning!). Did the usual checks, then temporarily connected the under floor heating load just to see the current draw. 18 amps at one stat point and and 21 amps going through another. That's either a lot of under floor heating or there is some other fault. At these 2 point there are 2 pairs of cables going down to the under floor heating (2.5mm flat coming in to supply it). I was wondering does anyone know anywhere where I can get a 2 zone thermostat. in other words one stat, with 2 switching points so the load can be switched by 2 contacts rather than the entire load going through one.

    Any ideas?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think you're going to struggle to find any standard room thermostat that can switch 18 or 21 Amps directly. I just had a look through my Orbis and Honeywell catalogues and 15 or 16 Amps is the max contact switching capacity, the majority are actually 5, 8 or 10 Amp. You're probably going to need relays or small contactors but how much room have you got to play with? I've got a feeling the heaters are incorrectly installed, 18 and 21 Amps sounds way too high for a domestic underfloor heating in a single circuit.
    _______________________________________________

    _______________________________________________

  3. #3
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Yep that's what i thought. Going to take the new Thermal imaging camera and see just how much of the floor is covered by underfloor heating. I estimate you would have to have 20 square meters to draw that much current. Some of the points where teh stats are have 2 cables going down floor. From there I don't know what happens yet. I haven't heard back from the customer so i'm guessing that someone provided him with some standard 16 amp stats and they should be melting anytime soon.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by skatingsparks View Post
    ...... I haven't heard back from the customer...
    Maybe not hearing back from the customer would be the preferrable outcome with this particular job.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. [Question] LED strips over heating
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 05-Jul-14, 07:35 PM
  2. lighting/ heating tip
    By murdock in forum Energy and Resource Conservation Forum
    Replies: 1
    Last Post: 09-Jul-11, 01:05 PM
  3. Pool Heating
    By daveob in forum Energy and Resource Conservation Forum
    Replies: 2
    Last Post: 22-Sep-10, 08:43 AM
  4. Floor-crossing season.
    By Dave A in forum General Chat Forum
    Replies: 22
    Last Post: 24-Nov-08, 09:33 AM
  5. Are our politicians still stuck in another time zone?
    By duncan drennan in forum South African Politics Forum
    Replies: 0
    Last Post: 13-Sep-07, 09:05 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •