I agree, above 2.5mm they may not be solid, 2.5mm and below they may be solid or stranded.
House wire, which is a single core cable or GP wire, has strands greater in size than 0.5mm.
I hope that is correct, as then it would differentiate between single core cable and flexible cable, the strands of which are between 0.5mm and 0.3mm.
Smaller than 0.3mm and that is classified as a flexible cord.
Trying to get this right in my head as I once saw a house wires with "single core cables" in conjutes, but the strands of the cable were very fine and less than 0.5mm, much less. I see this as illegal
Annealed copper is just the heating process it goes through to make it flexible. A busbar for example isn't annealed, it's what's referred to as hard-drawn copper. Cabtyre is made from stranded annealed copper.
I would disagree. I don't think that because the rule states Conductors of nominal cross-sectional area exceeding 2,5 mm2 shall be stranded, you can infer from it that conductors less than the size stated must not be stranded.6.3.2.1 Conductors of nominal cross-sectional area exceeding 2,5 mm2
shall be stranded,
I believe this to mean that conductors less than, and including 2.5mm, shall not be stranded.
seems like they dont anneal the new cables...have you tried to bend one recently.
I would say the only reason you can't use cabtyre as installation cabling is that being fine stranded it's not suitable for the terminations in sockets, switches and circuit breakers. I suppose if you bootlace ferrule all terminations I don't see where there's a rule that would exclude it for any other reason.
6.1.11 excludes it, except for certain conditions. cabtyre up to 4mm is classified as flexible cord.