    intrinsic relays

    heres one for the master sparkies;
    i want to convert a machine for a zoned area.its a few motors that can be changed to exd motors and some limit/level switches.my question is: can i install an intrinsic relay in the safe area to monitor the switch,without changing the switch to an ex rated switch.
    if it must be replaced then i wouldnt need the intrinsic relay in the first place.

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    you can use an intrisically safe relay but the relay cannot be in the zoned area...if it is located in the zoned area must be enclosed in a suitable enclosure.

    i did a job in cape town where our controls panel was mounted in a zoned area...so we had to install a panel which weighed about 400 kg and had a about 30 screws to hold the front cover.

  3. #3
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    hi murdock the relay will be in the safe area,but i see there are some other dis.boards in zone 2, but protected by purging and others with lel sensors.
    i am leaving the selection of the level switches to the consultants. they can sort out the zoning and loop diagrams,etc