    flexible cables

    is it legal to install sabs approved flexible cables from a main DB to a sub DB.

    in other words run a circuit directly from a new DB installed in a basement

    via a 21 core sabs approved flexible cable

    then disconnect the existing circuits in the sub DB on the first floor and join then directly to the 21 core flex cable straight to the dedicated socket outlets...which are wired in house wire.

    how important are the numbers in the flexible cable?

    this is not a trick question i am

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    please note pg 84 of sans 6.1.11 flexible cords shall not be used as part of the elctrical installtion, except where...

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,403
    Thanks
    513
    Thanked 854 Times in 687 Posts
    As far as I'm aware you're not permitted to use flexible cords (cabtyre) between a main and sub DB. It's not just 0142 regs that forbid this, also IEC 60335-1. If I remember correctly, ammendment 3 clarified.
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  4. #4
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    this thread is gona get interesting...busy with the generator thread have been all afternoon so once i have sorted that out i will come back to this thread.

  5. #5
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    826
    Thanks
    15
    Thanked 112 Times in 90 Posts
    Far as I know all cabling used should be SABS but, that does not mean it can be used for any purpose. The permanent installation far as I know should be "hard" wire.

  6. #6
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    what is important is understanding what the difference is in the definitions

    a cable...solid or stranded...with strands exceeding 0.51 mm

    flexible cable...consists of strands of diameter not exceeding 0.51mm and which th nominal cross section area of each conductor exceeds 4 mm square

    flexible cord...nominal cross sectional area of each conductor does not exceed 4 mm square and each conductor consists of strands of diameter less than 0.31mm

    6.1.11 flexible cords shall not be used as part of the electrical installation except a-e in sans code