  1. #11
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Even surface mount there is a correct and an incorrect way to do it. Moving it will also require it to be certified because the circuit is being extended. From what I hear the issueing of the COC can cost R500 with the work even being done.

  2. #12
    New Member
    Join Date
    Oct 2010
    Location
    Gauteng
    Posts
    4
    Thanks
    1
    Thanked 0 Times in 0 Posts

    plug points

    I am renovating the kitchen and as a result I need to re-position some sockets/plugpoints on the concrete walls. Some points need to be moved higher, for eg. eye-level oven connection and microwave connection by minimum 500 mm. I would like to know the average costs per point. I do understand that costs would vary, depending on the the distance also.

  3. #13
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Chase, fit conduit and box, wire, return to fit plug point and connect - probably something in the region of R400 to R800 per point, assuming your general contractor does the plastering in. There is an issue of scale. Two points are going to cost more per point than 20.

    If you're using a stove socket outlet, that'll cost more. Those stove sockets aren't nearly as cheap as plug points.
    Last edited by Dave A; 16-Oct-10 at 05:47 AM.

  4. Thanks given for this post:

    Capybara (17-Oct-10)

  5. #14
    New Member
    Join Date
    Oct 2010
    Location
    Gauteng
    Posts
    4
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Cost per plug point.

    Thanks a lot.

  6. #15
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Just keep in mind, a cooker plug is for free standing only. An ELO requires hard wire from the isolator. Remember too that NO socket outlets are allowed on the cooker circuit.

  7. #16
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    elo and hob you can reduce the wire and circuit breaker size from 40 to 30 amp and use 4 mmm wire.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Electrical Installation Costs
    By Tracsec in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 28-Jul-22, 05:38 AM
  2. Issuing electrical COCs - On a hiding to nothing!
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 18-Feb-12, 11:49 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •