    Box earthing

    Hi all

    The regs state that metal enclosures on pvc conduit should be earthed if they can become live and touched.6.12.3.1.
    What if the metal enclosure (4x4 box,4x2 box,round box for lights are on bosal or black enamel steel conduit .Would the boxes still need to be bonded /earthed if the switch ,light or plug that connects onto the box is earthed at the there earth terminal.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  2. #2
    Platinum Member SilverNodashi's Avatar
    Join Date
    May 2007
    Location
    Johannesburg, South Africa
    Posts
    1,197
    Thanks
    12
    Thanked 188 Times in 136 Posts
    As far as I understand, if the metal conduit is earthed, that would be fine. Otherwise you would need to earth the metal conduit as well.

  3. Thanks given for this post:

    Gtfast (31-Mar-17)

  4. #3
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks .It seems there are different methods of earthing the steel box .Just need some clarification .Some say the earthed switch, socket ,light that fits onto the box renders the box earthed.I earth the box with a separate earth from the earth terminal of the switch ,socket ,light that fits onto the box via lug and bolt is this necessary.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  5. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Apologies that was already answered.Let me rephrase .I understand the conduit cannot be used as an earth .So is the box earthed if the conduit is earthed.Does one have to earth the box separately.

    Sent from my HUAWEI VNS-L31 using Tapatalk

Similar Threads

  1. Earthing
    By TECHNICIAN 810 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 04-Apr-23, 04:53 AM
  2. Earthing problem while doing a COC
    By Tonye in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 29-Nov-16, 10:22 AM
  3. Earthing equipment questions
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 26
    Last Post: 22-Nov-15, 10:51 AM
  4. Another earthing question
    By adrianh in forum Technology Forum
    Replies: 6
    Last Post: 16-Feb-14, 05:03 PM
  5. Earthing and the CoC
    By WallyL in forum General Regulatory Compliance Forum
    Replies: 11
    Last Post: 20-Jan-11, 12:06 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •