    Conduit cross sectional area

    Hi all
    As per the 6.5.6.3 Multicore cables in wireways.
    When working out the cross sectional area of conduit does one use the inner or outer diameter .This is in order to acertain how many multi core cables one can insert into the conduit .

    Sent from my HUAWEI VNS-L31 using Tapatalk

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Surely the reg can only be referring to the space available which is the cross sectional area of the void inside the conduit ie work out the available area from the internal radius (half internal diameter) using Pi R squared.
    _______________________________________________

    _______________________________________________

  3. Thanks given for this post:

    Gtfast (31-Mar-17)

  4. #3
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks Andy
    That is my understanding.

    Sent from my HUAWEI VNS-L31 using Tapatalk
    Last edited by Dave A; 21-Jan-17 at 05:18 AM. Reason: merge of two posts

  5. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    What does one do with regards to stove connections where 6mm flat twin and earth is used in 20mm conduit ,which seems to be the norm .According to calculation it is very border line in fact the cable is a bit big.20mm conduit is 90.75mms with internal radius 8,5mm and the cable is 93,8mms with values 13,4mm *7mm as per Aberdare specs.When doing a COC how does one deal with this.It seems 25mm conduit should be used or change cable to single cores or am I missing something.This also effects if 20 mm flexible conduit is used from isolator to stove 25mm pvc flex conduit should be used or use 6mm single cores

    Sent from my HUAWEI VNS-L31 using Tapatalk
    Last edited by Gtfast; 20-Jan-17 at 08:40 AM.

  6. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Gtfast View Post
    ..........20mm conduit is 90.75mms with internal radius 8,5mm.........
    If a 20mm conduit has an internal radius of 8.5mm then;
    8.5 squared = 72.25,

    multiply that by pi,
    72.25 x 3.14159 = 226.68mm²

    I don't think you need to be that accurate, you can round up to 227mm² to make the calculations easier.

    If the CSA of the 6mm cable is 93.8mm² then the conduit will be 41% filled.

    6.5.6.3 Multicore cables in wireways
    To determine the size of wireway needed to accommodate cables of different
    sizes, add up the overall nominal cross-sectional area of each cable and
    ensure that this total area does not exceed the following percentages of
    cross-sectional area of the wireway:
    a) 40 % for conduit;
    b) 35 % for ducting; and
    c) 45 % for trunking.
    So the conduit would be 1% 'overfilled'....would this be something I'd personally fail on a CoC?...Probably not, I think the discrepency is too small to warrent remidial action. If the radius of the conduit is actually 1/100th of a milimeter larger than you measured (8.51mm) then it would be within the 40% full requirement. I wouldn't consider a conduit being 1/100th of a milimeter too small to be something worth quibbling about.
    _______________________________________________

    _______________________________________________

  7. Thank given for this post:

    ACEsterhuizen (27-Jan-17), Dave A (23-Jan-17), Gtfast (31-Mar-17)

  8. #6
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks Andy
    With you on that one.

    Sent from my HUAWEI VNS-L31 using Tapatalk

  9. #7
    New Member
    Join Date
    Mar 2015
    Location
    Queenstown
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi colleagues, I read your comments above and am still lost a bit. My confusion is around Reg 6.5.6.3 which talks about overrall nominal cross sectional area of each cable. How do I work overall cross-sectional area of 2.5mm2 flat twin & earth, for example? Because 2.5mm2 referers to each core inside that insulation sheath, but excludes insulation sheath itself.

  10. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yes, the 2.5mm² refers to the CSA of the copper conductor. For the cross-sectional area of the entire cable including the insulation and sheath you'd need to refer to the manufacturers data sheet.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Surfix only through a wall without conduit.
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 16-Jan-20, 07:26 PM
  2. Too many cables in conduit
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 12-Mar-19, 09:02 AM
  3. [Question] Can plumbing pipes (copper etc) be installed next to and behind my DB & across my conduit?
    By ACEsterhuizen in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Jan-16, 09:15 AM
  4. Metal conduit argument
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 19-Jul-13, 11:11 PM
  5. Rates on Sectional Title Units
    By Sieg in forum General Business Forum
    Replies: 1
    Last Post: 29-Aug-08, 01:14 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •