    Some simple words that can save you a lot of grief

    Hi

    On a quotes I do for electrical works I am very glad I had, in the terms and conditions of the quote, the words -

    'Any part of the existing installation which is to be added to or altered is assumed to be compliant with current SANS 10142 standards'

    It can get you out of trouble if you find lots of problems once you start.

    A job I quoted on looked neat, tidy and proper. I took a few covers off to have a look before quoting. The client wanted some alterations which were pretty standard. It's only when the faithful fluke 1653B was brought in we found SO many problems which caused the client to get upset and go after the guy who had done the original works.

    We found that pretty much every single point had an earth wire in it, but stopped (cut) a couple of inches outside of the various points. You looked in the box and it looked new and neat, pulled the earth wire and found it was just there for show, just went into the conduits a little way and stopped. DB board the same!

    Yes, he had a COC.

    No, he was not happy.

    No, I can't believe people would cut such corners to save a few bucks.

  2. Thank given for this post:

    DieterT (16-Oct-15), tec0 (12-Oct-15)

  3. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by skatingsparks View Post
    We found that pretty much every single point had an earth wire in it, but stopped (cut) a couple of inches outside of the various points. You looked in the box and it looked new and neat, pulled the earth wire and found it was just there for show, just went into the conduits a little way and stopped. DB board the same!
    ...
    No, I can't believe people would cut such corners to save a few bucks.
    Neither can I. That's criminal!

  4. #3
    Diamond Member tec0's Avatar
    Join Date
    Jun 2009
    Location
    South Africa
    Posts
    4,624
    Thanks
    1,884
    Thanked 463 Times in 410 Posts
    Blog Entries
    3


    I actually know for a fact that that is not the first time... I recall doing contract work "i was tiling the bathroom" When i saw a something scary... You know that nice thick red wire and black wire they use for Live and neutral? Well they only go in for about 10cm and then is spliced with a normal twin-flex speaker wire... I told the owner and well... He blew wasn't very happy...

    I highly recommend checking ALL the wires... But not bother actually installing the earth wire... Well that is low...
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

  5. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yep it's illegal but not that uncommon. I've come across installations where there's 25mm wiring at an isolator switch and it's been ferruled onto 4mm wiring a few inches into the conduit and same again at the DB. The original issue was low voltage causing the machine to shut down intermittently and the sparky that installed it had been back and bypassed the safety system which caused complete motor failure. It was only when loop impedance tests made no sense that we decided to replace the 40 meters of wiring we discovered the joints and the undersized wiring. We couldn't even get the 4mm wires out of the conduit because they'd gone rigid and hard with the heat.
    _______________________________________________

    _______________________________________________

  6. #5
    Diamond Member tec0's Avatar
    Join Date
    Jun 2009
    Location
    South Africa
    Posts
    4,624
    Thanks
    1,884
    Thanked 463 Times in 410 Posts
    Blog Entries
    3
    Got this from a friend a month ago.

    Right what do you think is missing here...

    That Thud you heard was my IQ... There is no trip-switch of any kind... This is part of a much larger and more scary picture but i took the really scary stuff out...

    Before i forget it his 3 Phase

    Click image for larger version. 

Name:	wire.jpg 
Views:	200 
Size:	45.2 KB 
ID:	5974
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

Similar Threads

  1. Replies: 4
    Last Post: 17-Apr-11, 12:55 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •